Right, and back to Pete's point, so long as a building is furnished with
a sprinkler system in accordance with the code, 13 or 13R, it's
considered to be "protected throughout".

Steve Leyton




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Roland Huggins
Sent: Friday, August 01, 2014 12:22 PM
To: [email protected]
Subject: Re: 6 Story Hotel

I think the only two trade-ups that require a full 13 system is:

1 - increase in fire area for type of construction

2- reduction in the rating of passive construction


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 1, 2014, at 11:31 AM, Sharon Alves <[email protected]>
wrote:

> However, if the architect is using a fire sprinkler system in lieu of
height or type of construction, etc. it must then be a full 13 system.
> 