Maybe [F] 903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in Group R occupancies up to and including four stories in height shall be permitted to be installed throughout in accordance with NFPA 13R.
However, and as noted in the commentary; "it must be noted that although the building would be considered sprinklered throughout in accordance with NFPA-13R, NOT ALL OF THE CODE SPRINKLER ALTERNATIVES could be applied. Any alternative that requires the installation of an NFPA-13 system would not be applicable if a portion of the building utilizes an NFPA-13R system." Again aside from 510 special provisions........... 504.2 Building Height - 903.3.1.1 NFPA-13...........Except Group R - 13R recognized, 20 Feet, 1 Story with a maximum 4 stories and 60 feet. 506.3 Building Area Increase - 903.3.1.1 NFPA-13 508.4 Occupancy Separation - 903.3.1.1 NFPA-13.....however designer could still have separated occupancies with 13R utilizing the non sprinklered column and a 2 hr separation. Theres more.................... John Drucker, CET Assistant Construction Official Fire Protection Subcode Official Building/Fire/Electrical Inspector Borough of Red Bank Red Bank, New Jersey Email: [email protected] Cell/Text: 732-904-6823 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Friday, August 1, 2014 3:20 PM To: [email protected] Subject: Re: 6 Story Hotel there's no dispute as to whether Table 508.4 requires a full 13 system. The question is does the IBC consider a building with a 13R system to be protected throughout. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Aug 1, 2014, at 12:13 PM, Duane Johnson <[email protected]> wrote: > The note at the bottom of Table 508.4 states: S = Buildings equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1. > > 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Section 903.3.1.1.1. > > Note, it does not reference 903.3.1.2 which is for NFPA 13R sprinkler systems. > > Duane Johnson, PE _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org