[F] 903.3.1.2 NFPA 13R sprinkler systems. Automatic sprinkler systems in
Group  R occupancies up to and including four stories in height shall be
permitted to be installed throughout in accordance with NFPA 13R.

However, and as noted in the commentary;  "it must be noted that although
the building would be considered sprinklered throughout in accordance with
NFPA-13R, NOT ALL OF THE CODE SPRINKLER ALTERNATIVES could be applied. Any
alternative that requires the installation of an NFPA-13 system would not be
applicable if a portion of the building utilizes an NFPA-13R system."

Again aside from 510 special provisions...........

504.2 Building Height - 903.3.1.1 NFPA-13...........Except Group R - 13R
recognized, 20 Feet, 1 Story with a maximum 4 stories and 60 feet.

506.3 Building Area Increase - 903.3.1.1   NFPA-13

508.4 Occupancy Separation - 903.3.1.1 NFPA-13.....however designer could
still have separated occupancies with 13R utilizing the non sprinklered
column and a 2 hr separation.

Theres more....................

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Friday, August 1, 2014 3:20 PM
To: [email protected]
Subject: Re: 6 Story Hotel

there's no dispute as to whether Table 508.4 requires a full 13 system.  The
question is does the IBC consider a building with a 13R system to be
protected throughout.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 1, 2014, at 12:13 PM, Duane Johnson <[email protected]>
wrote:

> The note at the bottom of Table 508.4 states: S = Buildings equipped
throughout with an automatic sprinkler system installed in accordance with
Section 903.3.1.1.
> 
> 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code
require that a building or portion thereof be equipped throughout with an
automatic sprinkler system in accordance with this section, sprinklers shall
be installed throughout in accordance with NFPA 13 except as provided in
Section 903.3.1.1.1.
> 
> Note, it does not reference 903.3.1.2 which is for NFPA 13R sprinkler
systems.
> 
> Duane Johnson, PE

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to