there’s no dispute as to whether Table 508.4 requires a full 13 system.  The 
question is does the IBC consider a building with a 13R system to be protected 
throughout.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 1, 2014, at 12:13 PM, Duane Johnson <[email protected]> wrote:

> The note at the bottom of Table 508.4 states: S = Buildings equipped 
> throughout with an automatic sprinkler system installed in accordance with 
> Section 903.3.1.1.
> 
> 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code 
> require that a building or portion thereof be equipped throughout with an 
> automatic sprinkler system in accordance with this section, sprinklers shall 
> be installed throughout in accordance with NFPA 13 except as provided in 
> Section 903.3.1.1.1.
> 
> Note, it does not reference 903.3.1.2 which is for NFPA 13R sprinkler systems.
> 
> Duane Johnson, PE

_______________________________________________