Duane-
I've sent him a copy of our calc's showing exactly what you described with the 
flat line, he's still convinced that the added flow (250) will required more 
pressure. Not that it's totally accurate I told him to think of the fire truck 
as a pump and it was providing the pressure for the outside hose streams...

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Tuesday, November 18, 2014 2:05 PM
To: [email protected]
Subject: RE: Hose added to calc's. no PSI

We allow for the fire department to fight the fire while the sprinklers are 
activated. So, while the sprinklers are flowing at X psi @ Y gpm, the fire 
department will open up a fire hydrant to flow additional gpm. The pressure 
they use is less than the sprinkler requirements. Therefore we need to account 
for additional gpm, but not additional psi. Show him a graph with the 
horizontal line at the top of the sprinkler demand...

Duane Johnson, PE
Design Manager
Strickland Fire Protection
301-474-1136 Office
301-455-0010 Cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, November 18, 2014 1:59 PM
To: [email protected]
Subject: Hose added to calc's. no PSI

I've been trying to explain to a civil engineer that we (fire sprinkler) 
include outside hose allowance into our calc's but only for the extra gpm, not 
as far as additional psi goes. I'm sure it's the way I'm trying to explain it 
that's not making any sense to him, can one of you more versed in the English 
language help me out and put it in layman's terms for me?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to