You have already answered the question by referring to the fire truck as a
pump, which it is. If more pressure is needed,they simply pump it.

Lamar Vaughn, SET

On Tue, Nov 18, 2014 at 2:15 PM, Brian Harris <[email protected]>
wrote:

> Duane-
> I've sent him a copy of our calc's showing exactly what you described with
> the flat line, he's still convinced that the added flow (250) will required
> more pressure. Not that it's totally accurate I told him to think of the
> fire truck as a pump and it was providing the pressure for the outside hose
> streams...
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Duane Johnson
> Sent: Tuesday, November 18, 2014 2:05 PM
> To: [email protected]
> Subject: RE: Hose added to calc's. no PSI
>
> We allow for the fire department to fight the fire while the sprinklers
> are activated. So, while the sprinklers are flowing at X psi @ Y gpm, the
> fire department will open up a fire hydrant to flow additional gpm. The
> pressure they use is less than the sprinkler requirements. Therefore we
> need to account for additional gpm, but not additional psi. Show him a
> graph with the horizontal line at the top of the sprinkler demand...
>
> Duane Johnson, PE
> Design Manager
> Strickland Fire Protection
> 301-474-1136 Office
> 301-455-0010 Cell
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Tuesday, November 18, 2014 1:59 PM
> To: [email protected]
> Subject: Hose added to calc's. no PSI
>
> I've been trying to explain to a civil engineer that we (fire sprinkler)
> include outside hose allowance into our calc's but only for the extra gpm,
> not as far as additional psi goes. I'm sure it's the way I'm trying to
> explain it that's not making any sense to him, can one of you more versed
> in the English language help me out and put it in layman's terms for me?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to