In your calculations you provide X gallons for firedepartment use, after you have used up Y gallons for the sprinkler system. Thefire department takes that X gallons from a hydrant through their Fire Truckmounted pump. The pump operator delivers the X gpm through the hoses at whateverPSI is their operating standard, the pressure being supplied by the truckmounted pump.
Richard L. Mote CET Designer / Retired -----Original Message----- From: Brian Harris <[email protected]> To: sprinklerforum <[email protected]> Sent: Tue, Nov 18, 2014 1:58 pm Subject: Hose added to calc's. no PSI I've been trying to explain to a civil engineer that we (fire sprinkler) include outside hose allowance into our calc's but only for the extra gpm, not as far as additional psi goes. I'm sure it's the way I'm trying to explain it that's not making any sense to him, can one of you more versed in the English language help me out and put it in layman's terms for me? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org