John Drucker <[email protected]<mailto:[email protected]>> wrote:


Aaron,
Back in the day I worked as a fitter for Allied Fire and Safety (now in Neptune 
NJ) the wise guys (and I mean it that way) I worked with always carried extra 
coupons on a piece of bailing wire in truck just in case one got lost. With 
that I learned they meant absolutely nothing. It is what it is. As for 
mechanical fittings and flow switches, the first is easily seen not made up and 
the second easily tested via the ITC. Roustabouts and Morton salt also come to 
mind. Good inspectors who know what they're looking for make sure things are 
right in the end, coupons or not.
Some story from AvalonBay.
John Drucker - Mobile Email
Fire Protection Inspector
Red Bank, New Jersey
[email protected]<mailto:[email protected]><mailto:[email protected]<mailto:[email protected]>>
Cell/Text 732-904-6823
Aaron Peck <[email protected]<mailto:[email protected]>> wrote:
That's why the hole saw should have a pilot bit for getting the coupon back
out. Also any fitting that knows what he's doing has a strung together mass
of coupons for every pipe size. For the "just in case" you lose the coupon,
albeit not from leaving inside the piping but rather losing it after you
remove it.
Or rather I hope it's not from losing it inside the pipe.
Correct me if I'm wrong but I believe there is a requirement for proving
that the hole is actually cut and the switch or tee is not just stuck on the
pipe. I seem to remember that. And the code didn't say how you prove it but
that having the coupon attached to the device or fitting "proved" that.
--
Aaron Peck, SET  •  Fire Protection Engineering Technologist
NICET Certified NFPA Member
Skype: (202) 407-9079 • Cambodia: (+855) 78700407
**Currently in Manama, Bahrain UTC/GMT +3:00 hours (8 Hours ahead of EST)**
            **Bahrain Number #(+973)39605669 Skype forwards to this #**
-----Original Message-----
From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
On Behalf Of JD Gamble
Sent: Thursday, February 19, 2015 8:46 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Mech Tee Installation
Thanks for all the insight.  It would appear that there is no "code" for the
display of the coupon, just a measure of "good practice".
-----Original Message-----
From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
On Behalf Of [email protected]<mailto:[email protected]>
Sent: Wednesday, February 18, 2015 10:35 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Mech Tee Installation
Every time I see the coupon, I wonder if it is the coupon from that pipe and
that hole.  I also wonder, how do  you retrieve the coupon from a riser?
Douglas Hicks
General Fire Equip Co of Eastern Oregon, Inc
> I agree with all the should's.  Hanging the cutout is a fantastic
> idea, ain't required though which was the original question.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com><http://www.burnsmcd.com>
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work
> For
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]<mailto:[email protected]>]
>  On Behalf Of
> rongreenman .
> Sent: Wednesday, February 18, 2015 9:38 PM
> To: 
> [email protected]<mailto:[email protected]>
> Subject: Re: Mech Tee Installation
>
> There is the requirement, as mentioned, for a coupon retrieval system
> on the Above Ground Test Certificate. there should then be a shop SOP
> and a field SOP. Attaching the coupon to the tee is a pretty good SOP
> for the field work.
>
>
> On Wed, Feb 18, 2015 at 5:12 PM, Cahill, Christopher
> <[email protected]<mailto:[email protected]>>
> wrote:
>
>> What's the difference between the field cut and the shop cut? There
>> isn't an AHJ in the world that can tell if I shop drilled or field
>> drilled.  At my last company often enough we'd shop drill. Or the
>> shop welded cut out?
>> Or is someone saying they all need to be attached?  I don't see where
>> any need be. And the requirements for retrieval in no way shape or
>> form requires attachment.  How exactly to you show compliance with
>> the dimensions for groove depth and width, thread specs, etc?  'Cuz
>> you know to an extent there is slop in these and they hold at least
>> for a while outside specs. Do ya'll hang gauge templates to every
>> fitting to show compliance?
>> Do you hang a weld x-ray on each weld?  'Cuz you know there are
>> requirements that can't be readily seen if they are in compliance.
>> Do you hang the ball peen hammer next to the 'fixed' dripping welds
>> that occasionally occur?
>>
>> Every seen the weld scraping from the factory produced pipe get
>> dropped and adhered to the inside of the next pipe in the formation
>> line?  Now if I knock them loose I can show they were removed by
>> attaching. Wonder how you show compliance if they didn't occur in the
>> first place?
>>
>> My real point in my ramblings is there comes a place where we have to
>> trust all involved did their job right.  Do things get left in the
>> pipe occasionally?  Sure do, but we need to tackle keeping the valve
>> open before we get into the minutia of the other possible failures
>> which all together don't add up to a lot of failures.
>>
>> Chris Cahill, PE*
>> Associate Fire Protection Engineer
>> Burns & McDonnell
>> Phone:  952.656.3652
>> Fax:  952.229.2923
>> [email protected]<mailto:[email protected]>
>> www.burnsmcd.com<http://www.burnsmcd.com><http://www.burnsmcd.com>
>> *Registered in: MN
>>
>>
>> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work
>> For
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]<mailto:[email protected]>]
>>  On Behalf Of Kenneth
>> Berman
>> Sent: Wednesday, February 18, 2015 6:32 PM
>> To: 
>> [email protected]<mailto:[email protected]>
>> Subject: Re: Mech Tee Installation
>>
>> attaching the coupon shows compliance with retrieval requirement.
>> 2007
>> 13-
>> 6.5.5.2<http://6.5.5.2>(2) Might as well hang it there, it's just trash.
>>
>> On Wed, Feb 18, 2015 at 5:26 PM, John Denhardt <
>> [email protected]<mailto:[email protected]>
>> > wrote:
>>
>> > No reference in NFPA 13 that I'm aware.  Usually see the
>> > requirement in a specification.  You might want to look at a
>> > manufacturer's installation instruction sheet that is part of the
>> > listing for the
>> device.
>> >
>> > John
>> >
>> > -----Original Message-----
>> > From: Sprinklerforum [mailto:
>> > [email protected]<mailto:[email protected]>]
>> >  On Behalf Of JD
>> > Gamble
>> > Sent: Wednesday, February 18, 2015 6:08 PM
>> > To: 
>> > [email protected]<mailto:[email protected]>
>> > Subject: Mech Tee Installation
>> >
>> > Does anyone know the actual Code for requiring the attachment of a
>> > drill out to a Mech Tee?
>> >
>> >
>> >
>> > I know its good practice, but does anyone know the actual code, or
>> > is there one?
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> > Life Safety Solutions of Sheridan
>> >
>> > JD Gamble
>> >
>> > [email protected]<mailto:[email protected]> 
>> > <mailto:[email protected]<mailto:[email protected]>>
>> >
>> > (307) 763-3361
>> >
>> >
>> >
>> >
>> >
>> > ---
>> > This email has been checked for viruses by Avast antivirus software.
>> > http://www.avast.com
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]<mailto:[email protected]>
>> >
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>> > n kl er.org<http://er.org> _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]<mailto:[email protected]>
>> >
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>> > n
>> > kl
>> > er.org<http://er.org>
>> >
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l er.org<http://er.org> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org<http://er.org>
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]<mailto:[email protected]>
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org<http://er.org> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org<http://er.org>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to