We have an existing fire service (from city water main) feeding hydrants and
sprinkler systems. The hydrant at the end of this fire service (hydrant #1)
has a static of 50psi, residual of 40psi, and a flow of 750gpm. 

Our client wants to add an additional water source, via a 200,000 gallon
water storage tank at 610 feet about the POC, hoping that the pressure will
increase. This storage tank also feeds existing hydrants. The closest
hydrant from this water source (hydrant #2) is 50 feet higher in elevation
than hydrant #1. Hydrant #2 has a static of 128psi, residual of 8psi, and a
flow of 265gpm.  To connect the two water sources we are going to run a new
fire line 380 lineal feet from hydrant #1 to hydrant #2. We use HydraCalc
and it does not allow two separate water sources.  

Any suggestions on how to determine how much the pressure will be increased,
if any?

Thanks,

 

 

Paul B. Cetani

 <mailto:[email protected]> [email protected]

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to