Check with tech support at HydraTec I believe you can have as many as 5 sources if you input them right. Richard L. Mote CET Retired -----Original Message----- From: Paul Cetani <[email protected]> To: Sprinklerforum <[email protected]> Cc: rocci3 <[email protected]> Sent: Thu, Feb 19, 2015 4:43 pm Subject: Hydraulic Calculations with two water sources
We have an existing fire service (from city water main) feeding hydrants and sprinkler systems. The hydrant at the end of this fire service (hydrant #1) has a static of 50psi, residual of 40psi, and a flow of 750gpm. Our client wants to add an additional water source, via a 200,000 gallon water storage tank at 610 feet about the POC, hoping that the pressure will increase. This storage tank also feeds existing hydrants. The closest hydrant from this water source (hydrant #2) is 50 feet higher in elevation than hydrant #1. Hydrant #2 has a static of 128psi, residual of 8psi, and a flow of 265gpm. To connect the two water sources we are going to run a new fire line 380 lineal feet from hydrant #1 to hydrant #2. We use HydraCalc and it does not allow two separate water sources. Any suggestions on how to determine how much the pressure will be increased, if any? Thanks, Paul B. Cetani <mailto:[email protected]> [email protected] CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org