Paul - If I am reading this correctly, these are two gravity-fed systems. One 
with a higher pressure head than the other.  But in theory the higher tank will 
simply drain until its elevation is equal to the lower tank. Or as Charles 
illustrated, if you have a check valve separating the systems, the higher 
system will be your source until it drains to the point that they are at equal 
pressures. In the end, you will have a higher pressure with lower volume; then 
when the pressures equalize, your volume will increase a little but at the 
lower tank pressure.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Paul Cetani
Sent: Thursday, February 19, 2015 3:44 PM
To: [email protected]
Cc: [email protected]
Subject: Hydraulic Calculations with two water sources

We have an existing fire service (from city water main) feeding hydrants and 
sprinkler systems. The hydrant at the end of this fire service (hydrant #1) has 
a static of 50psi, residual of 40psi, and a flow of 750gpm.

Our client wants to add an additional water source, via a 200,000 gallon water 
storage tank at 610 feet about the POC, hoping that the pressure will increase. 
This storage tank also feeds existing hydrants. The closest hydrant from this 
water source (hydrant #2) is 50 feet higher in elevation than hydrant #1. 
Hydrant #2 has a static of 128psi, residual of 8psi, and a flow of 265gpm.  To 
connect the two water sources we are going to run a new fire line 380 lineal 
feet from hydrant #1 to hydrant #2. We use HydraCalc and it does not allow two 
separate water sources.

Any suggestions on how to determine how much the pressure will be increased, if 
any?

Thanks,





Paul B. Cetani

 <mailto:[email protected]> [email protected]



CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to