Hey Brad,
This test was conducted by the water company and doesn't really sound right
to us either but, because of the water situation in California, they will
not perform a new test.

Paul B. Cetani
Exec. Vice President

Nor Cal Fire, Inc.
16840 Joleen Way, Bldg A
Morgan Hill, CA 95037
T 408-776-1580
F 408-776-1590
[email protected]
www.norcalfire.com

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Friday, February 20, 2015 6:08 AM
To: [email protected]
Subject: RE: Hydraulic Calculations with two water sources


Paul,

I am curious about the hydrant #2 flow test:

"The closest hydrant from this water source (hydrant #2) is
50 feet higher in elevation than hydrant #1. Hydrant #2 has a static of
128psi, residual of 8psi, and a flow of 265gpm."

If you have time will you post any additional details you know about it
please?

thanks,
Brad

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to