You're welcome Paul, I had fun-- my first two-source calc!

If it is close to correct and you connect hyd #1 to hyd #2 with 6.11 x 380
feet with 2 ells, hyd #2 is 50 feet above hyd #1, and the original flow
tests of #1= (50,40,750) and #2= (128,8,265) are accurate, and the Water
Dept let's you use enough of 'their' water to let you flush, test, and
re-flow test, I think what will happen is:

 

@ Hyd #1--- 150,40,996

@ Hyd #2--- 128,20,772

 

I sooo wanted to meet with the Water Dept and ask, "was someone here
intentionally this cruel to that fire plug or has there been some horrible
accident"?

 

:) Brad

 

----------------------------------------------------------------------------
-------------------------------------------------------------------------

Hi Brad,
I didn't realize that attachments weren't allowed. As it turns out, the fire
department just required the installation of the line connecting the two

supplies and we will see what happens. Thanks for your help...

 