Hello Mark!

Thanks- it is an interesting problem and I have tried to figure it out up
one side and down the other. I think if everyone turned their water off
while I got a true Static it would be higher. And if they left it off while
I measured 265 GPM @ 8 PSI wouldn't the drop be greater (drop being the sum
of the velocity head and the friction head)? So you are right because under
those conditions I would state as being "fact" a storage tank that is higher
AND farther away than the first one :) (I think).

I am now dwelling on Paul's original "... storage tank at 610 feet about the
POC...". I thought he must have meant above instead of about, and in Kansas
610 feet above the POC means "upstream" of the POC because we don't even
have buildings that tall here. But names like Nor Cal and Morgan Hill got me
thinking it might really be above, and if so the new tank would make the
"static" 610x.433= 264 PSI at the POC, which would be an increase.

thanks again man,
Brad  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Saturday, February 21, 2015 1:17 PM
To: [email protected]
Subject: Re: Hydraulic Calculations with two water sources

Hi Brad and all,
I think you're missing the fact that the city water main serves many(maybe
thousands) of users between the possibly elevated tank and hydrant #2. The
static pressure you're reading at that hydrant is actually the residual
pressure remaining in the line after many thousand GPM is distributed to
users along the way. Without knowing all those flow points (hydraulic nodes)
it is impossible for you to calculate the information you are presenting as
fact. Aside from that, I agree that a meeting with the water purveyor is a
necessary step in the design. 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Feb 21, 2015, at 9:59 AM, "Brad Casterline" <[email protected]>
wrote:
> 
> Paul,
> 
> I have been thinking more about this and re-reading the excellent
responses
> and learning. I think it is important to get an accurate sketch before you
> finalize the calculations. I would want to meet with the water department
> and draw the picture the numbers and your current understanding show for
> Hydrant #2:
> If the source for #2 is a storage tank its elevation would be 128/.433=
~296
> feet above the hydrant. It would also be about 10 miles away because
flowing
> 265 through 6" UG (minimum if serving hydrants) it would take about 60,000
> feet of pipe and fittings to burn 120 PSI. This is not impossible but it
is
> strange that after all that the FD is left with 8 psi at 265 GPM to try to
> do something with, when 376 feet over and 50 feet down is hydrant #1 with
40
> @ 750!
> 
> thanks and good luck,
> Brad
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]]
> On Behalf Of Brad Casterline
> Sent: Friday, February 20, 2015 10:02 AM
> To: [email protected]
> Subject: RE: Hydraulic Calculations with two water sources
> 
> Thanks Paul. The first thing I noticed yesterday was that the static
> difference between #1 and #2 did not correspond to the elevation
difference.
> And 120 PSI worth of Pf+Pv from the source to the hydrant is 5-6 times
more
> than one would expect if it is serving hydrants.
> I can see 128,108,265. Is there any way something might have been jotted
> down wrong when the information was communicated?
> 
> Brad  
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]]
> On Behalf Of Paul Cetani
> Sent: Friday, February 20, 2015 9:12 AM
> To: [email protected]
> Subject: RE: Hydraulic Calculations with two water sources
> 
> Hey Brad,
> This test was conducted by the water company and doesn't really sound
right
> to us either but, because of the water situation in California, they will
> not perform a new test.
> 
> Paul B. Cetani
> Exec. Vice President
> 
> Nor Cal Fire, Inc.
> 16840 Joleen Way, Bldg A
> Morgan Hill, CA 95037
> T 408-776-1580
> F 408-776-1590
> [email protected]
> www.norcalfire.com
> 
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information 
> belonging to the sender. The information is intended only for the use of
> individual or entity named above. If you are not the intended recipient,
or
> the employee or agent responsible to deliver this message to the intended
> recipient, you are hereby notified that any disclosure, copying or taking
of
> any action in reliance on the contents of this information is strictly
> prohibited. If you have received this transmission in error, please
> immediately notify us by telephone to arrange for return of the documents.
> 
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]]
> On Behalf Of Brad Casterline
> Sent: Friday, February 20, 2015 6:08 AM
> To: [email protected]
> Subject: RE: Hydraulic Calculations with two water sources
> 
> 
> Paul,
> 
> I am curious about the hydrant #2 flow test:
> 
> "The closest hydrant from this water source (hydrant #2) is
> 50 feet higher in elevation than hydrant #1. Hydrant #2 has a static of
> 128psi, residual of 8psi, and a flow of 265gpm."
> 
> If you have time will you post any additional details you know about it
> please?
> 
> thanks,
> Brad
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to