Obstruction requirements for sprinklers are based on the sprinkler and the
potential obstruction, not on the occupancy below. If the potential obstruction
is not there, don't worry about it.
Also, I would contact the client's FM Global rep and have him/her develop the
requirements for sprinklers beneath the cable trays. FM will need to be
satisfied so you might as well have them give you the requirements up front. Just because it is not specifically addressed in 2.0 does not mean they won't
have an opinion.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Thu, Jun 11, 2015 at 6:57 AM, [email protected]
<[email protected]> wrote:
I'm did the research yesterday in FM 2-0 and in the AFSA informal interps,
but I wanted to make sure I'm not missing something here...

Can I get a confirmation that you are still required to meet obstruction
criteria for ESFR (storage) sprinkler heads even when they're being used to
protect a non-storage occupancy?

I see nothing in 2-0 about the use of storage sprinkler in non-storage
occupancies, but I know that NFPA 13 covers this. I think that the listing
criteria of the ESFR heads is what drives the obstruction rules, so these
must be complied with to use the heads for say, a manufacturing occupancy.

Backstory: we have a customer that is converting rack storage to
manufacturing, and they're putting in a lot of cable trays for the
machinery. Wide cable trays, double stacked cable trays, offset trays,
etc. Nothing over 10 feet wide, but very full cable trays that almost
always are over 2 feet wide. The building is about 24' high, and the trays
will be down at 12' so plenty of clear space.

The customer is FM insured, so we're giving them the option to either
install barriers under the trays and space the roof-level sprinklers every
8 ft or to leave the barriers out and put the roof-level heads under the
trays every 4 ft (and also following the maximum square footage allowances
in FM 2-0 of course).

Before I deliver this great news, I just wanted to make sure I didn't miss
something in my reading of 2-0.

I'm guessing, as well, that I can simply ignore the obstruction rules
relating to the placement of obstructions over flue spaces and other
storage-specific items.

Thanks in advance for any assistance with this!

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to