You make me sound like the Soup Nazi - lmao. My closer friends on the Forum make a point of beating me about the head and shoulders every chance they get. Even Brad and I occasionally exchange emails off Forum and he’s the closest I have ever come to trying to skin someone alive and I don’t expect him to agree with me either. So any time the mood strikes, break out the bat. I currently don’t see where we have a disagreement unless you are saying that the obstruction rules for ESFR are not required to be applied.
FM and NFPA 13 criteria have diverged in their individual methodologies and the two are now so different that they’re effectively speaking different languages. NFPA 13 has allowed ESFR and CMSA to be used in ordinary hazard occupancies for some time (typically expected to occur when an occupancy change occurs with an existing system). It wasn’t until the 2013 edition that their use in a light hazard occupancy was blessed (see section 12.6.7). With NFPA 13 being the standard required by the building codes, we still have to ensure that the requirements of 13 are also satisfied. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jun 11, 2015, at 12:45 PM, Damien Shannon <[email protected]> wrote: > > Now I know for sure that I have been specifically warned not to disagree > with Roland :) however just to throw my 2 cents in... > > My understanding is that if you are utilizing FM Datasheets, that really we > shouldn't be using the term ESFR (although manufacturer's datasheets still > title them as such). However it is not a term used in FM 2-0/8-9. Rather > they simply use the term 'Storage' or Non-Storage'. In the FM Listing > section of some ESFRs (e.g. > http://www.vikinggroupinc.com/databook/sprinklers/storage/060198.pdf > <http://www.vikinggroupinc.com/databook/sprinklers/storage/060198.pdf>), they > are specifically listed for Non-Storage as well as Storage. My > understanding is that you can utilize these sprinklers per the requirements > of Tables 1-3 of FM 2-0 and the respective obstruction criteria when > dealing with HC1 thru HC3 occupancies. The K-Factors in those table (HC 1 > thru 3) would indicate that they are including 'ESFR' (aka Storage) > sprinklers in their HC1 thru HC3 criteria. > > With all respect. > > Damien Shannon. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org