If you're going to rework the existing ESFR system and respace the sprinklers 
why not just change them out to a non-ESFR sprinkler?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

On Thu, Jun 11, 2015 at 6:57 AM, [email protected]
<[email protected]> wrote:
I'm did the research yesterday in FM 2-0 and in the AFSA informal interps, but 
I wanted to make sure I'm not missing something here...

Can I get a confirmation that you are still required to meet obstruction 
criteria for ESFR (storage) sprinkler heads even when they're being used to 
protect a non-storage occupancy?

I see nothing in 2-0 about the use of storage sprinkler in non-storage 
occupancies, but I know that NFPA 13 covers this. I think that the listing 
criteria of the ESFR heads is what drives the obstruction rules, so these must 
be complied with to use the heads for say, a manufacturing occupancy.

Backstory: we have a customer that is converting rack storage to manufacturing, 
and they're putting in a lot of cable trays for the machinery. Wide cable 
trays, double stacked cable trays, offset trays, etc. Nothing over 10 feet 
wide, but very full cable trays that almost always are over 2 feet wide. The 
building is about 24' high, and the trays will be down at 12' so plenty of 
clear space.

The customer is FM insured, so we're giving them the option to either install 
barriers under the trays and space the roof-level sprinklers every
8 ft or to leave the barriers out and put the roof-level heads under the trays 
every 4 ft (and also following the maximum square footage allowances in FM 2-0 
of course).

Before I deliver this great news, I just wanted to make sure I didn't miss 
something in my reading of 2-0.

I'm guessing, as well, that I can simply ignore the obstruction rules relating 
to the placement of obstructions over flue spaces and other storage-specific 
items.

Thanks in advance for any assistance with this!

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to