Now I know for sure that I have been specifically warned not to disagree with Roland :) however just to throw my 2 cents in...
My understanding is that if you are utilizing FM Datasheets, that really we shouldn't be using the term ESFR (although manufacturer's datasheets still title them as such). However it is not a term used in FM 2-0/8-9. Rather they simply use the term 'Storage' or Non-Storage'. In the FM Listing section of some ESFRs (e.g. http://www.vikinggroupinc.com/databook/sprinklers/storage/060198.pdf), they are specifically listed for Non-Storage as well as Storage. My understanding is that you can utilize these sprinklers per the requirements of Tables 1-3 of FM 2-0 and the respective obstruction criteria when dealing with HC1 thru HC3 occupancies. The K-Factors in those table (HC 1 thru 3) would indicate that they are including 'ESFR' (aka Storage) sprinklers in their HC1 thru HC3 criteria. With all respect. Damien Shannon. On 11 June 2015 at 20:24, Roland Huggins <[email protected]> wrote: > I don’t see how you can NOT comply with all requirements assigned to ESFR > sprinklers. They are a suppression mode sprinkler with a smaller remote > area so must knock down the fire quickly. Obstructions are a huge issue. > It’s not really a content driven thing since Class I commodities have a > similar density demand to OHG1 and it still has to comply with the same > obstruction rules. Granted the difference it fire growth rate and HRR will > impact the issue but most likely it will be in how quickly the system FAILS > and not whether the system will fail. > > Consider yourself confirmed (that and a dollar will get you a cup of > coffee) > > Roland > > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > > > On Jun 11, 2015, at 9:35 AM, Ben Young <[email protected]> > wrote: > > > >> Can I get a confirmation that you are still required to meet obstruction > >> criteria for ESFR (storage) sprinkler heads even when they're being > used to > >> protect a non-storage occupancy? > >> > >> I see nothing in 2-0 about the use of storage sprinkler in non-storage > >> occupancies, but I know that NFPA 13 covers this. I think that the > listing > >> criteria of the ESFR heads is what drives the obstruction rules, so > these > >> must be complied with to use the heads for say, a manufacturing > occupancy. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- *Damien Shannon* _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org