I don’t see how you can NOT comply with all requirements assigned to ESFR sprinklers. They are a suppression mode sprinkler with a smaller remote area so must knock down the fire quickly. Obstructions are a huge issue. It’s not really a content driven thing since Class I commodities have a similar density demand to OHG1 and it still has to comply with the same obstruction rules. Granted the difference it fire growth rate and HRR will impact the issue but most likely it will be in how quickly the system FAILS and not whether the system will fail.
Consider yourself confirmed (that and a dollar will get you a cup of coffee) Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jun 11, 2015, at 9:35 AM, Ben Young <[email protected]> wrote: > >> Can I get a confirmation that you are still required to meet obstruction >> criteria for ESFR (storage) sprinkler heads even when they're being used to >> protect a non-storage occupancy? >> >> I see nothing in 2-0 about the use of storage sprinkler in non-storage >> occupancies, but I know that NFPA 13 covers this. I think that the listing >> criteria of the ESFR heads is what drives the obstruction rules, so these >> must be complied with to use the heads for say, a manufacturing occupancy. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org