I don’t see how you can NOT comply with all requirements assigned to ESFR 
sprinklers.  They are a suppression mode sprinkler with a smaller remote area 
so must knock down the fire quickly.  Obstructions are a huge issue.  It’s not 
really a content driven thing since Class I commodities have a similar density 
demand to OHG1 and it still has to comply with the same obstruction rules.  
Granted the difference it fire growth rate and HRR will impact the issue but 
most likely it will be in how quickly the system FAILS and not whether the 
system will fail.

Consider yourself confirmed (that and a dollar will get you a cup of coffee)

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jun 11, 2015, at 9:35 AM, Ben Young <[email protected]> wrote:
> 
>> Can I get a confirmation that you are still required to meet obstruction
>> criteria for ESFR (storage) sprinkler heads even when they're being used to
>> protect a non-storage occupancy?
>> 
>> I see nothing in 2-0 about the use of storage sprinkler in non-storage
>> occupancies, but I know that NFPA 13 covers this. I think that the listing
>> criteria of the ESFR heads is what drives the obstruction rules, so these
>> must be complied with to use the heads for say, a manufacturing occupancy.