Just make sure they don't need it to be a rated partition. Only the tyco window sprinklers provide a fire rating. Otherwise you are just providing a water curtain around the opening per NFPA 13.
Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.526.7443 cell www. AFPsprink.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Gregory Lindholm Sent: Wednesday, September 02, 2015 6:26 AM To: SprinklerFORUM Subject: Atrium We have a new school that has a three story atrium, and the Architect is asking for us to protect the third floor glass with sprinklers place a maximum of 6' on center, and not more than 12" off the glass. I originally assumed that we would use the Tyco Window Sprinklers, but the windows on this project has multiple horizontal mullions in the windows (4 or 5).lowed with the Tyco heads. I was thinking of just deigning it as a Water Curtain, with the regular heads at 6' on center, with 3 gpm per lineal foot. Thoughts? Greg Lindholm _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org