This is an interesting thread.  There is Tyco's specific application window 
sprinkler, which has been tested and listed for protecting a glazed barrier (to 
keep it from becoming a ~crazed~ barrier).  With the listing comes 
restrictions, e.g. no horizontal mullions.  Then there is IBC's prescription 
for "sprinklers" with a performance based requirement to wet the entire glass 
surface.

Without full-scale tests proving a certain arrangement of standard sprinklers 
can protect glazing with horizontal mullions, I would be forced to put 
sprinklers at the top and at every horizontal mullion level.

J. Scott Mitchell, PE
Fire Protection Engineer | 
Projects Engineering
CNS Pantex | 806.477.5883 | 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, September 03, 2015 8:15 AM
To: [email protected]
Subject: RE: Atrium

I agree with Geoff. The problem remains the total wetting of the glass. This 
cannot be achieved with the horizontal mullions in  place. Moreover, can 
"entire surface of the glass" be wetted using standard sprinklers in a water 
curtain arrangement as opposed to listed window sprinklers?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ken Holsopple
Sent: Wednesday, September 02, 2015 11:24 AM
To: [email protected]
Subject: RE: Atrium

Roland,

I don't disagree but.....

If Section 404.6  (see below) of the IBC prescribes the closely spaced 
sprinklers and the architect choses that instead of the other options listed to 
protect the atrium, then is it that big of a jump to apply Sections 8.15.4 and 
11.3.3 out of NFPA 13? (2007 edition.)

I only ask because the commentary in the 2007 handbook seems to allude that the 
requirement to provide the curtains is driven by the building code(s) and the 
NFPA 13 gives the how to.

404.6 Enclosure of atriums. Atrium spaces shall be separated from adjacent 
spaces by a I-hour fire barrier constructed in accordance with Section 707 or a 
horizontal assembly constructed in accordance with Section 712, or both.

Exceptions:
   1. A glass wall forming a smoke partition where automatic sprinklers are 
spaced 6 feet (1829 mm) or less along both sides of the separation wall, or on 
the room side only if there is not a walkway on the atrium side, and between 4 
inches and 12 inches (102 mm and 305
mm) away from the glass and designed so that the entire surface of the glass is 
wet upon activation of the sprinkler system without obstruction. The glass 
shall be installed in a gasketed frame so that the framing system deflects 
without breaking (loading) the glass before the sprinkler system operates.

    2. A glass-block wall assembly in accordance with Section
2110 and having a 3/4-hour fire protection rating.

     3. The adjacent spaces of any three floors of the atrium shall not be 
required to be separated from the atrium where such spaces are accounted for in 
the design of the smoke control system.

Funny how the IBC doesn't mention how many sprinklers are required to be 
calculated. Is a calc even necessary or is it implied that you go to NFPA 13 
for that?

Best Regards,
Ken Holsopple

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, September 02, 2015 10:57 AM
To: [email protected]
Subject: Re: Atrium

proceed with caution least you own the responsibility for something that might 
leave a bad taste.  This isn’t really defined by NFPA 13 so what is your basis? 
 The industry use to be (often still is) a little casual about extending the 
age old guidance from NFPA 101 allowed ONLY for atrium glass to any and all 
glass.  Even there it does say the ENTIRE glass shall be wetted. It was amusing 
that a couple of cycles ago NFPA 80A simply required a Water Curtain for 
exterior exposure protection.  That would work well on a 4 story structure.   
13 refined it’s exposure protection criteria and part of that was to address 
run down and associated ledges and mullions.  It allows rather large 
protrusions but the exposure will be different than an interior fire (so don’t 
casual embrace the sizes it states).  The Tyco WS sprinkler is rather 
particular about mullions too.  Sounds like a common thread not to be lightly 
ignored.

So what level of insurance do you have for performing engineering since it is 
not prescriptively defined by NFPA 13?  If the architect wants it, let them 
design/stamp it.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Sep 2, 2015, at 4:25 AM, Gregory Lindholm <[email protected]> wrote:
>
> We have a new school that has a three story atrium, and the Architect is 
> asking for us to protect the third floor glass with sprinklers place a 
> maximum of 6' on center, and not more than 12" off the glass.
> I originally assumed that we would use the Tyco Window Sprinklers, but the 
> windows on this project has multiple horizontal mullions in the windows (4 or 
> 5).lowed with the Tyco heads.
> I was thinking of just deigning it as a Water Curtain, with the regular heads 
> at 6' on center, with 3 gpm per lineal foot.
> Thoughts?
>
> Greg Lindholm
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to