proceed with caution least you own the responsibility for something that might 
leave a bad taste.  This isn’t really defined by NFPA 13 so what is your basis? 
 The industry use to be (often still is) a little casual about extending the 
age old guidance from NFPA 101 allowed ONLY for atrium glass to any and all 
glass.  Even there it does say the ENTIRE glass shall be wetted. It was amusing 
that a couple of cycles ago NFPA 80A simply required a Water Curtain for 
exterior exposure protection.  That would work well on a 4 story structure.   
13 refined it’s exposure protection criteria and part of that was to address 
run down and associated ledges and mullions.  It allows rather large 
protrusions but the exposure will be different than an interior fire (so don’t 
casual embrace the sizes it states).  The Tyco WS sprinkler is rather 
particular about mullions too.  Sounds like a common thread not to be lightly 
ignored.

So what level of insurance do you have for performing engineering since it is 
not prescriptively defined by NFPA 13?  If the architect wants it, let them 
design/stamp it.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Sep 2, 2015, at 4:25 AM, Gregory Lindholm <[email protected]> wrote:
> 
> We have a new school that has a three story atrium, and the Architect is 
> asking for us to protect the third floor glass with sprinklers place a 
> maximum of 6' on center, and not more than 12" off the glass.
> I originally assumed that we would use the Tyco Window Sprinklers, but the 
> windows on this project has multiple horizontal mullions in the windows (4 or 
> 5).lowed with the Tyco heads.
> I was thinking of just deigning it as a Water Curtain, with the regular heads 
> at 6' on center, with 3 gpm per lineal foot.
> Thoughts?
> 
> Greg Lindholm                                           
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to