No, it's a stand alone. No domestic service. 

Sent from my iPhone

> On Oct 5, 2015, at 10:57 AM, Steve Leyton <st...@protectiondesign.com> wrote:
> 
> Good points, which also beg the question:  Does the 2" meter also feed
> the domestic water?   If so, you can take the handles off the
> double-check, or lock them open if they're not already or ... or ... 
> 
> Really, if you have questions about that basis of design or want to play
> the part of community gadfly, take it to the AHJ.
> 
> SL
> 
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> Larry Keeping
> Sent: Monday, October 05, 2015 10:50 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Monitoring 13D control valves in California 
> 
> If I've read things correctly the only shutoff to the system is at the
> BFP which serves 5 units. 
> 
> Since 13D in Section 6.2.3 says that where more than one dwelling unit
> are served by the same water supply, each unit must have its own
> individual control valve, so I am having trouble seeing the set up
> described as a 13D system.
> 
> It looks like a 13R application to me.
> 
> Larry Keeping
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> firs...@aol.com
> Sent: October-05-15 1:44 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Monitoring 13D control valves in California 
> 
> It appears that both the AHJ and contractor  have made mistakes on this
> project. I am interested in finding out what exactly happened. We should
> all play by the same rules. Im trying to figure out what is correct here
> according to standard, CFC & CBC. Like I said, it looks like a 13R but
> now they're saying its a 13D without DCVA monitoring. 
> 
> Sent from my iPhone
> 
>>> On Oct 5, 2015, at 9:48 AM, Steve Leyton <st...@protectiondesign.com>
>> wrote:
>> 
>> Are you doing a 3rd party inspection or some sort of risk
> management/loss prevention analysis?  Why not just call the AHJ or
> installing contractor and ask for approved basis of design?
>> 
>> SL
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum on behalf of firs...@aol.com
>> Sent: Mon 10/5/2015 9:37 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: Monitoring 13D control valves in California
>> 
>> Hi Steve, thanks for responding. Isn't the CBC more restrictive
> therefore you can't allow something less? This particular system looks
> like a 13R but they failed to provide electrical for tamper switches. So
> now they argue it is a 13D serving a building with 5 townhouse's
> separated by 1 hour construction. My thinking is since it is 5 units,
> not one or two family dwelling, the exception for electrical monitoring
> does not apply. Therefore tampers are required. Am I correct?   
>> 
>> Sent from my iPhone
>> 
>>> On Oct 5, 2015, at 8:52 AM, Steve Leyton <st...@protectiondesign.com>
> wrote:
>>> 
>>> It's possible the AHJ has accepted these to be of limited area if the
> 
>>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple 
>>> solutions for "monitoring", including the locking of valves.  Perhaps
>>> the AHJ approved an alternative to electronic supervision.   
>>> 
>>> Steve L.
>>> 
>>> 
>>> 
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>>> firs...@aol.com
>>> Sent: Monday, October 05, 2015 7:38 AM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: Monitoring 13D control valves in California
>>> 
>>> The California Building Code requires sprinkler control valves to be 
>>> electrically monitored. One of the exceptions is One and Two Family 
>>> Dwellings, 13D.
>>> 
>>> What if it is a stand alone 13D system? (2" water meter with one DCVA
> 
>>> to a 2" underground, serving a row of 5 town homes with one hour 
>>> separations between units. The 2" underground branches off to each
> unit.
>>> Each unit has it's own flow switch and test valve).
>>> 
>>> The exception specifically states for one and two family dwellings 
>>> because the control valve is before the domestic service so shutting 
>>> off the sprinklers shuts off the domestic therefor it is self
> monitoring.
>>> The stand alone serving 5 units does not have this valve arrangement 
>>> therefore it would require electric monitoring per CBC.
>>> 
>>> Am I thinking correctly? According to CBC the two control valves on 
>>> the DCVA would need tampers, correct?
>>> 
>>> Owen Evans
>>> 
>>> Sent from my iPad
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> ler
>>> .org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> ler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to