That's the thing Steve, I don't think there's a way to determine if the 
overhead sprinklers will reach the lowest rack levels (without performing 
expensive tests, lol)... 
So then the answer is to install ESFR sprinklers throughout.

Thanks Steve and say hi to the old gang for Stephanie and I!

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Sorrell
Sent: Thursday, October 29, 2015 10:59 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

You would install the ESFR sprinklers below the solid catwalk if the catwalk 
would not allow the discharge from the overhead ESFR system to reach the 
protected commodity below.


Stephen J. Sorrell, CET
NICET# 77901 Level III
E mail: [email protected]
Design Manager

Performance Fire Protection, LLC
Corporate Office
179 Gasoline Alley -  PO Box 4510
Mooresville, NC 28117
Phone: 704-663-1664  Fax: 704-663-1652
Cell : 704-309-1242 

Web: www.performancefire.com
Licensed in NC, SC, VA, TN, GA, AL

"Performance on Every Level."

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Wednesday, October 28, 2015 3:45 PM
To: [email protected]
Subject: ESFR Sprinklers and covered catwalks

Hello everybody,

I have a situation where a client is looking to install an ESFR system 
protecting racks... they would like to add a solid floor catwalk system between 
the racks. Do you continue installing ESFR sprinklers under each level or can 
you install control mode sprinkler under the catwalks while the ESFR's at the 
ceiling protect the commodity?? 
I did look up the archives and a few people have asked similar questions over 
the years, but I don't see an answer... 
NFPA 13, 2007 ed. 

Thank you in advance!
Steven 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to