The catwalk is no different than any other obstruction within the area, right? For any other obstruction you would use the same ESFR's below the obstruction as you used at the ceiling/roof.
Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Mackinnon Sent: Wednesday, October 28, 2015 3:45 PM To: [email protected] Subject: ESFR Sprinklers and covered catwalks Hello everybody, I have a situation where a client is looking to install an ESFR system protecting racks... they would like to add a solid floor catwalk system between the racks. Do you continue installing ESFR sprinklers under each level or can you install control mode sprinkler under the catwalks while the ESFR's at the ceiling protect the commodity?? I did look up the archives and a few people have asked similar questions over the years, but I don't see an answer... NFPA 13, 2007 ed. Thank you in advance! Steven _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org