The conversation in the office kept going back to hvac ductwork and how you 
would place an ESFR sprinkler underneath when it became an obstruction... 
Normally there will be commodity stored under the duct, but in this situation, 
no stock will be in the catwalks, just the racks... so the additional ESFR 
sprinklers will spray the catwalks and not necessarily the commodity...  is 
this over kill??

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, October 29, 2015 11:13 AM
To: [email protected]
Subject: RE: ESFR Sprinklers and covered catwalks

The catwalk is no different than any other obstruction within the area, right?  
For any other obstruction you would use the same ESFR's below the obstruction 
as you used at the ceiling/roof.


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Wednesday, October 28, 2015 3:45 PM
To: [email protected]
Subject: ESFR Sprinklers and covered catwalks

Hello everybody,

I have a situation where a client is looking to install an ESFR system 
protecting racks... they would like to add a solid floor catwalk system between 
the racks. Do you continue installing ESFR sprinklers under each level or can 
you install control mode sprinkler under the catwalks while the ESFR's at the 
ceiling protect the commodity?? 
I did look up the archives and a few people have asked similar questions over 
the years, but I don't see an answer... 
NFPA 13, 2007 ed. 

Thank you in advance!
Steven 



_______________________________________________