Was it ever permitted for a 1000 GPM pump to be supplied by 6" piping?
Also, was it ever permitted to put a CONCENTRIC 8x6 reducer on the
suction flange of a pump.
We have an existing project where the owner was hoping to remove the
pump and to supply from city water. I informed them that the water
pressures on site were not compatible. They also have a pump that has
been requiring a lot of maintenance. As I looked at the as-built plans
(yeah, miraculously they had them for a building built in 1988), it
shows a 6" supply for the 1000 gpm pump and the concentric reducer on
the suction flange of the pump.
In the most recent editions of NFPA 20, a 1000 gpm pump needs an 8"
suction line.
--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org