Was it ever permitted for a 1000 GPM pump to be supplied by 6" piping? Also, was it ever permitted to put a CONCENTRIC 8x6 reducer on the suction flange of a pump.

We have an existing project where the owner was hoping to remove the pump and to supply from city water. I informed them that the water pressures on site were not compatible. They also have a pump that has been requiring a lot of maintenance. As I looked at the as-built plans (yeah, miraculously they had them for a building built in 1988), it shows a 6" supply for the 1000 gpm pump and the concentric reducer on the suction flange of the pump.

In the most recent editions of NFPA 20, a 1000 gpm pump needs an 8" suction line.

--
Travis Mack, SET