Thanks for the nod Scott.
For horizontal split case centrifugal supplied by storage tank only, psig
can actually drop below zero psi...
How much?  h=v^2/2g :)
On Feb 11, 2016 4:16 PM, "Travis Mack, SET" <[email protected]> wrote:

> I have yet to get any pump test information, but I assume it has been
> tested properly.
>
> Thanks for the confirmation of the reducers.  I was pretty certain that
> you couldn't use a concentric back in the day, but I didn't have the
> standard to verify it.
>
> What's funny is the pump is 8x6.  They ran a 6" underground and piping up
> to the suction of the pump, then had to put an 8x6 flanged "increaser" to
> match up with the pump.  You would think that some one would have had the
> idea back then that this didn't seem quite right.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/11/2016 3:12 PM, Scott Futrell wrote:
>
>> I thought Brad would have the suction size answer!
>>
>> Suction size has been for some time based upon the pressure remaining
>> above 0 psi when flowing at 150 percent of the rated capacity.  So, 6"
>> might be possible, but you'd have to verify the supply.
>>
>> Agree completely, no concentric on suction side.
>>
>> Scott
>>   Office: (763) 425-1001 x 2
>> Cell: (612) 759-5556
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Brad
>> Casterline
>> Sent: Thursday, February 11, 2016 4:08 PM
>> To: [email protected]
>> Subject: Re: NFPA 20 around 1988
>>
>> No to concentric on suction side---
>> Requires ECCENTRIC, top flat.
>> (if this is vertical in-line, different ballgame) On Feb 11, 2016 3:58
>> PM, "Travis Mack, SET" <[email protected]> wrote:
>>
>> Was it ever permitted for a 1000 GPM pump to be supplied by 6" piping?
>>> Also, was it ever permitted to put a CONCENTRIC 8x6 reducer on the
>>> suction flange of a pump.
>>>
>>> We have an existing project where the owner was hoping to remove the
>>> pump and to supply from city water.  I informed them that the water
>>> pressures on site were not compatible.  They also have a pump that has
>>> been requiring a lot of maintenance.  As I looked at the as-built
>>> plans (yeah, miraculously they had them for a building built in 1988),
>>> it shows a 6" supply for the
>>> 1000 gpm pump and the concentric reducer on the suction flange of the
>>> pump.
>>>
>>> In the most recent editions of NFPA 20, a 1000 gpm pump needs an 8"
>>> suction line.
>>>
>>> --
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to