Does 'totally aware of NPSH' mean you can tell me what causes cavitation?
On Feb 11, 2016 4:56 PM, "Travis Mack, SET" <[email protected]> wrote:

> Totally aware of NPSH, and calculating velocity in the suction piping and
> also how to read a table that indicates minimum sizes.
>
> The pump has been in service for years.  I assume that it has never drawn
> into negative suction pressures.  However, that still doesn't relieve the
> requirements to meet the tables in NFPA 20.  The system design was done by
> a technician and not a PE, so there is not the option to supercede the
> tables that provide minimum suction pipe sizing.  And since the velocity of
> 1500 gpm in 6" sch 10 piping is 15.2 fps, that exceeds the 15 fps limit set
> in 20.  So, regardless of NPSH or not, it exceeds the 15 fps and the tables
> in 20.
>
> Regardless, the pump has been problematic for the building owner and it
> will be replaced.  I was just curious based on the things I saw on it.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/11/2016 3:48 PM, Brad Casterline wrote:
>
>> As a Standard, 20 has to draw some lines somewhere Travis.
>> Brush up on NPSH.
>> Then, since you have as builts, maybe the pump data is around too.
>> The main thing is that available NPSH is equal to or greater than required
>> NPSH!
>> On Feb 11, 2016 4:40 PM, "Travis Mack, SET" <[email protected]> wrote:
>>
>> Even if the increaser is technically OK, the 6" suction pipe could be a
>>> problem.  I haven't calc'd it yet, but that may put the velocity in
>>> excess
>>> of 15 fps for the suction piping.
>>>
>>> I'm pretty certain they are going to replace the pump and just upsize the
>>> suction piping for the 10 pipe diameters to be in compliance with NFPA 20
>>> current edition.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> On 2/11/2016 3:35 PM, [email protected] wrote:
>>>
>>> Then technically that makes the "6x8 Increaser" okay doesn't it?
>>>> Mark at Aero
>>>> 602 820-7894
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]] On Behalf Of Travis
>>>> Mack, SET
>>>> Sent: Thursday, February 11, 2016 3:16 PM
>>>> To: [email protected]
>>>> Subject: Re: NFPA 20 around 1988
>>>>
>>>> I have yet to get any pump test information, but I assume it has been
>>>> tested properly.
>>>>
>>>> Thanks for the confirmation of the reducers.  I was pretty certain that
>>>> you couldn't use a concentric back in the day, but I didn't have the
>>>> standard to verify it.
>>>>
>>>> What's funny is the pump is 8x6.  They ran a 6" underground and piping
>>>> up
>>>> to the suction of the pump, then had to put an 8x6 flanged "increaser"
>>>> to
>>>> match up with the pump.  You would think that some one would have had
>>>> the
>>>> idea back then that this didn't seem quite right.
>>>>
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
>>>>
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>
>>>> On 2/11/2016 3:12 PM, Scott Futrell wrote:
>>>>
>>>> I thought Brad would have the suction size answer!
>>>>>
>>>>> Suction size has been for some time based upon the pressure remaining
>>>>> above 0 psi when flowing at 150 percent of the rated capacity.  So, 6"
>>>>> might be possible, but you'd have to verify the supply.
>>>>>
>>>>> Agree completely, no concentric on suction side.
>>>>>
>>>>> Scott
>>>>>     Office: (763) 425-1001 x 2
>>>>> Cell: (612) 759-5556
>>>>>
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum
>>>>> [mailto:[email protected]] On Behalf Of
>>>>> Brad Casterline
>>>>> Sent: Thursday, February 11, 2016 4:08 PM
>>>>> To: [email protected]
>>>>> Subject: Re: NFPA 20 around 1988
>>>>>
>>>>> No to concentric on suction side---
>>>>> Requires ECCENTRIC, top flat.
>>>>> (if this is vertical in-line, different ballgame) On Feb 11, 2016 3:58
>>>>> PM, "Travis Mack, SET" <[email protected]> wrote:
>>>>>
>>>>> Was it ever permitted for a 1000 GPM pump to be supplied by 6" piping?
>>>>>
>>>>>> Also, was it ever permitted to put a CONCENTRIC 8x6 reducer on the
>>>>>> suction flange of a pump.
>>>>>>
>>>>>> We have an existing project where the owner was hoping to remove the
>>>>>> pump and to supply from city water.  I informed them that the water
>>>>>> pressures on site were not compatible.  They also have a pump that
>>>>>> has been requiring a lot of maintenance.  As I looked at the as-built
>>>>>> plans (yeah, miraculously they had them for a building built in
>>>>>> 1988), it shows a 6" supply for the
>>>>>> 1000 gpm pump and the concentric reducer on the suction flange of the
>>>>>> pump.
>>>>>>
>>>>>> In the most recent editions of NFPA 20, a 1000 gpm pump needs an 8"
>>>>>> suction line.
>>>>>>
>>>>>> --
>>>>>> Travis Mack, SET
>>>>>> MFP Design, LLC
>>>>>> 2508 E Lodgepole Drive
>>>>>> Gilbert, AZ 85298
>>>>>> 480-505-9271
>>>>>> fax: 866-430-6107
>>>>>> email:[email protected]
>>>>>>
>>>>>> http://www.mfpdesign.com
>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>>>> l
>>>>>> er.org
>>>>>>
>>>>>> _______________________________________________
>>>>>>
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>> er.org _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org