No to concentric on suction side---
Requires ECCENTRIC, top flat.
(if this is vertical in-line, different ballgame)
On Feb 11, 2016 3:58 PM, "Travis Mack, SET" <[email protected]> wrote:

> Was it ever permitted for a 1000 GPM pump to be supplied by 6" piping?
> Also, was it ever permitted to put a CONCENTRIC 8x6 reducer on the suction
> flange of a pump.
>
> We have an existing project where the owner was hoping to remove the pump
> and to supply from city water.  I informed them that the water pressures on
> site were not compatible.  They also have a pump that has been requiring a
> lot of maintenance.  As I looked at the as-built plans (yeah, miraculously
> they had them for a building built in 1988), it shows a 6" supply for the
> 1000 gpm pump and the concentric reducer on the suction flange of the pump.
>
> In the most recent editions of NFPA 20, a 1000 gpm pump needs an 8"
> suction line.
>
> --