I have to say that my FAVORITE emails are the ones that contain the phrase, 
"Steve is correct."    I never get tired of reading that ...

SML

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Eggster
Sent: Tuesday, March 15, 2016 8:01 AM
To: [email protected]
Subject: Re: Standpipe Calc: Adding City Demand to Pumper Truck?

All that confirms my suspicions. I always calc to the FDC but when I came 
across these plans I tried to find justification in '14 and saw the material in 
the annex which set off a lot more questions.


Good to know guys,
thanks!


On Mon, Mar 14, 2016 at 4:13 PM, Tom Duross <[email protected]> wrote:

> Steve is correct.  A simple 151@0 to 150@1000 (or 1250) supply line, 
> regardless of city supply flow unless of course you can't supply the 
> pumper with 1000 or 1250 gpm supply.  The reason for the 150 psi 
> demand pressure is the system is hydro'd to 200.  You can use the two 
> (2) uppermost FDV's on the HMD standpipe flowing 250 each for the 
> standpipe required flow of 500 and then the uppermost FDV on each 
> remaining standpipe at 250 each to a max of 1000 for a sprinklered 
> building or 1250 for partially or a non-sprinklered building.  All 
> flows must have a minimum residual of 100 psi but I do what Steve says 
> and shoot for 105.  You can use K factors of 25 and
> 50 at the minimum residual of 105 to make your standpipe calc's easier 
> and the FDC is the supply point.  Remember not to calc a hole in the 
> pipe but to include the tee, nipple and valve.
> TD
>
>
> Tony:
>
> You (or the submitter) are over-simplifying what the annex says.  It's 
> not the intent that you take the city flow test and add it to the pumper 
> curve.
> NFPA 1901 sets the basic performance curve for a pumper at 150 PSI/1,000
> GPM.   NFPA 13E is the standard for FD Operations for buildings equipped
> with sprinklers and standpipes - that standard goes into the company 
> engineer's procedure for calculating the discharge pressure of the pump
> based on suction pressure, friction loss in hose and other variables.   But
> the bottom line is that it's all targeted at discharging 150 PSI 
> residual at
> 1,000 GPM.   This has NOTHING to do with pressure at the FDC; it has to do
> with calculating the performance of the apparatus.   What gets to the FDC
> is
> up to the engineer.
>
> Which is why 7.7.4 states, "When the system demand to be supplied by 
> the fire department at the fire department connection is being 
> determined, the local fire department shall be consulted regarding the water 
> supply
> available from a fire department pumper."    FROM A FIRE DEPARTMENT PUMPER.
> It's up to the incident commander and his or her engineer to determine 
> the suction pressure and set their discharge to whatever is required 
> to make their programmed starting pressure.  And based on the 
> nationwide standard and best practices, that is almost certain to be 
> 150 PSI at the prescribed flow rate.  The engineer will calculate the 
> friction loss in the discharge hose that's connected to the building.  
> If you are reviewing plans that show
> 150 PSI residual plus a positive suction head at that flow rate as the 
> inlet pressure, then that is almost certainly not correct.
>
> To answer your question, if I have a building with two (750 GPM) or 
> three or more (1,000 GPM) standpipes, we plug in a "flow test" static 
> pressure of
> 151
> PSI and a residual of 150 PSI at the target flow rate and we run the calc'
> using the FDC as the "city connection".    We plug in a 500 PSI hose stream
> allowance at the most remote standpipe outlets and at 250 GPM hose 
> streams at those points in the bulk main system where the other risers take 
> off.
> We
> allow 5 PSI for loss in a standard hose valve so the minimum pressure 
> at any node is 105 PSI.
>
> The foregoing is my opinion only and does not represent the opinion of 
> or any manner of interpretation by NFPA or the Technical Committee on 
> Standpipes.
>
> Steve Leyton
>
>
> Quick question: I'm reviewing some plans for a manual class I 
> standpipe and the designer added the city flow test to the usual 
> 1000gpm fire pumper curve in order to keep all the pipe down to 4". I 
> see in the NFPA 14 appendix that you can do this but personally I've 
> always just calculated solely to the pumper curve. How do you guys do 
> it?
>
> Also, I'm assuming that if you do factor in city supply wouldn't that 
> frequently require high pressure pipe and fittings depending on city 
> supply psi?
>
> _TONY
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to