I would consult the local FD and see what the fire pumper truck is rated
at. If they have a 1500 gpm pumper the curve might be more to your liking.

On Tue, Mar 22, 2016 at 8:31 AM, <[email protected]> wrote:

> Sorry for coming into this a week late.  We have recently been dealing
> with specs and AHJ requirements that state we need to supply 130psi and/or
> 140psi at the top outlet regardless of whether it is manual or automatic.
> Same flows as outlined in NFPA 14 (500gpm +250gpm per standpipe up to
> 1000gpm).  The fire pumper truck is still sized for 150psi @ 1000gpm.  What
> do you suggest we do if we can only set the FDC to be the source of 151@0
> and 150@1000?  Some building are still 70ft tall and the standpipe is
> still a manual wet.  Only accounting for elevation we are looking at
> 160psi/170psi demand at the FDC.  Even if your answer is make it an
> automatic standpipe, the 140psi requirement limits the "manual" standpipe
> building height to 23ft when we don't account for friction loss using your
> calculation procedure.  So we can't even meet these manual FDC 150psi calcs
> on a building that doesn't even need a standpipe.
>
> Thanks,
> Sean VG
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Steve Leyton
> Sent: Monday, March 14, 2016 3:57 PM
> To: [email protected]
> Subject: RE: Standpipe Calc: Adding City Demand to Pumper Truck?
>
> Tony:
>
> You (or the submitter) are over-simplifying what the annex says.  It's not
> the intent that you take the city flow test and add it to the pumper
> curve.  NFPA 1901 sets the basic performance curve for a pumper at 150
> PSI/1,000 GPM.   NFPA 13E is the standard for FD Operations for buildings
> equipped with sprinklers and standpipes - that standard goes into the
> company engineer's procedure for calculating the discharge pressure of the
> pump based on suction pressure, friction loss in hose and other variables.
>  But the bottom line is that it's all targeted at discharging 150 PSI
> residual at 1,000 GPM.   This has NOTHING to do with pressure at the FDC;
> it has to do with calculating the performance of the apparatus.   What gets
> to the FDC is up to the engineer.
>
> Which is why 7.7.4 states, "When the system demand to be supplied by the
> fire department at the fire department connection is being determined, the
> local fire department shall be consulted regarding the water supply
> available from a fire department pumper."    FROM A FIRE DEPARTMENT
> PUMPER.   It's up to the incident commander and his or her engineer to
> determine the suction pressure and set their discharge to whatever is
> required to make their programmed starting pressure.  And based on the
> nationwide standard and best practices, that is almost certain to be 150
> PSI at the prescribed flow rate.  The engineer will calculate the friction
> loss in the discharge hose that's connected to the building.  If you are
> reviewing plans that show 150 PSI residual plus a positive suction head at
> that flow rate as the inlet pressure, then that is almost certainly not
> correct.
>
> To answer your question, if I have a building with two (750 GPM) or three
> or more (1,000 GPM) standpipes, we plug in a "flow test" static pressure of
> 151 PSI and a residual of 150 PSI at the target flow rate and we run the
> calc' using the FDC as the "city connection".    We plug in a 500 PSI hose
> stream allowance at the most remote standpipe outlets and at 250 GPM hose
> streams at those points in the bulk main system where the other risers take
> off.  We allow 5 PSI for loss in a standard hose valve so the minimum
> pressure at any node is 105 PSI.
>
> The foregoing is my opinion only and does not represent the opinion of or
> any manner of interpretation by NFPA or the Technical Committee on
> Standpipes.
>
> Steve Leyton
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Tony Eggster
> Sent: Monday, March 14, 2016 3:24 PM
> To: [email protected]
> Subject: Standpipe Calc: Adding City Demand to Pumper Truck?
>
> Quick question: I'm reviewing some plans for a manual class I standpipe
> and the designer added the city flow test to the usual 1000gpm fire pumper
> curve in order to keep all the pipe down to 4". I see in the NFPA 14
> appendix that you can do this but personally I've always just calculated
> solely to the pumper curve. How do you guys do it?
>
> Also, I'm assuming that if you do factor in city supply wouldn't that
> frequently require high pressure pipe and fittings depending on city supply
> psi?
>
> _TONY
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to