Could be (I'll defer to the locals).

The one-piece thing is something I know the Air Force/ Air National Guard 
allows as a means to avoid a joint under aircraft hangar buildings. NFPA 
doesn't restrict the type of pipe under the building (as long as it's an 
approved fire protection pipe material).  Again, you may have engineer's 
preferences at work, or other agency requirements.


Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Rocci Cetani 3
Sent: Thursday, May 5, 2016 1:45 PM
To: [email protected]
Subject: RE: underground pipe under building footings

Mark- We are running under the entire ramp (about 18' long)  It's a switchback 
ramp so the (e) main will be running under the top landing of the ramp.  I 
don't design a lot of underground but when I do we have always been instructed 
to transition to DI or a 1 piece stainless steel  riser from our UG subs and or 
local FM's because the PVC isn't allow under the footings......is this maybe 
just a California thing?

Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


[email protected]
www.norcalfire.com

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, May 05, 2016 11:34 AM
To: [email protected]
Subject: RE: underground pipe under building footings

Rocci - There is no restriction regarding running lead-in piping under 
footings. The restriction is how far into the building you run the line. The 
concern is the damage created by the failure of a (normally) large diameter 
fire main, as well as the extensive downtime required to repair such a main if 
it were located a large distance from the outside of the building.
Generally speaking you are to bring the main up as close to the outside wall as 
practical given your circumstances. Exceptions are granted if you rout the pipe 
in a trench in the building floor with a removable cover.

NFA 24 or chapter 10 of NFPA 13 will give you this guidance.

In your situation I'd want to know if you are crossing under the narrow 
dimension of the ADA ramp or if the entire ramp covers the pipe.  In either 
case I don't think you violate NFPA guidance, per se.  But if there's a way to 
avoid having the entire ramp over this main it should be considered.
I.e., it's more of a best practices issue.


Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Thursday, May 5, 2016 1:24 PM
To: [email protected]
Subject: underground pipe under building footings

Before I go digging through a bunch of books I figured I'd try and save some 
time by asking all you EXPERTS.  Does anyone know which code states underground 
fire service can't run under footings? We have a project where a chemical 
bunker is being built and the ADA accessible ramp up to the bunker is being 
built  directly over an (e) 10" C-900 fire service and our new tap that is 
going to feed the system in the bunker.



Thanks in advance for your responses.



Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





[email protected]

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to