Rocci,
Chapter 80 of the CFC, page 513, revising section NFPA 13, 10.6.5,
"Pipe joints shall not be installed under foundation footings. The pipe
under the building or building foundation shall not contain mechanical
joints."
Also, on page 519, there's the same modification to NFPA 24, 10.6.5.
And, just to show you I know how to over-react, in a somewhat high
decibel conversation with one of the guys on the committee who made
those changes, I asked if that meant I couldn't use a flanged fitting,
as it wasn't a mechanical joint (mj) fitting.
His response was to make suggestions about my parents which I know
are not true as I have a photograph of their wedding. He later informed
me that it meant "any" joint under a building, and hung up.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 05/05/2016 2:59 PM, Rocci Cetani 3 wrote:
Thanks Steve, knew I could count on you!!! So I'm looking and can't seem to
find the actual code for the MJ restriction under buildings, you don't
happen to know it off the top of your head do you? Not sure if it's in CBC
or CFC but I'm looking through both.
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
[email protected]
www.norcalfire.com
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Thursday, May 05, 2016 1:43 PM
To: [email protected]
Subject: RE: underground pipe under building footings
We have state code amendments that further restrict NFPA 13/24 requirements.
No mechanical joints can be located under foundations or buildings, so you
either have to rise up outside and penetrate above the foundation or use a
one-piece in-building riser sweep to come up through the slab. These
provisions assume a riser located at the exterior perimeter of the building;
if you have to run piping underground, the same provisions apply in CA as in
the parent document. 10.6.2 states "Where approved ..." so this is up to
the AHJ in the first place. If special means and methods for protection of
the piping is acceptable to the AHJ, then (1), (2) and (3) may be applied
but that's all got to be done to a standard of care that is acceptable to
the AHJ. As a rule, most are spooked enough by the prohibition in 10.6.1
that they'll only accept engineered solutions so the "running pipe in
covered trenches" becomes a reinforced concrete chase that turns out to be a
deal-breaker in
just about every case. We've done it only on military projects in CA, and
that's been due to the anti-terrorism stuff in the UFC's where they want the
FLS systems components away from the exterior walls so they can't be
compromised by an attack on or an explosion outside of the building. In
those cases, the SEOR has made us a cool little concrete trench in which we
can run the pipe. A couple of our buildings were open uses so we didn't
even bury the pipe, just covered it with metal panels like grating or
diamond plate.
SL
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Thursday, May 05, 2016 12:13 PM
To: [email protected]
Subject: RE: underground pipe under building footings
Thanks Mark. Hopefully our California expert Steve Leyton chimes in.
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
[email protected]
www.norcalfire.com
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information belonging to the sender. The information is
intended only for the use of individual or entity named above. If you are
not the intended recipient, or the employee or agent responsible to deliver
this message to the intended recipient, you are hereby notified that any
disclosure, copying or taking of any action in reliance on the contents of
this information is strictly prohibited. If you have received this
transmission in error, please immediately notify us by telephone to arrange
for return of the documents.
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, May 05, 2016 12:00 PM
To: [email protected]
Subject: RE: underground pipe under building footings
Could be (I'll defer to the locals).
The one-piece thing is something I know the Air Force/ Air National Guard
allows as a means to avoid a joint under aircraft hangar buildings. NFPA
doesn't restrict the type of pipe under the building (as long as it's an
approved fire protection pipe material). Again, you may have engineer's
preferences at work, or other agency requirements.
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Thursday, May 5, 2016 1:45 PM
To: [email protected]
Subject: RE: underground pipe under building footings
Mark- We are running under the entire ramp (about 18' long) It's a
switchback ramp so the (e) main will be running under the top landing of the
ramp. I don't design a lot of underground but when I do we have always been
instructed to transition to DI or a 1 piece stainless steel riser from our
UG subs and or local FM's because the PVC isn't allow under the
footings......is this maybe just a California thing?
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
[email protected]
www.norcalfire.com
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information belonging to the sender. The information is
intended only for the use of individual or entity named above. If you are
not the intended recipient, or the employee or agent responsible to deliver
this message to the intended recipient, you are hereby notified that any
disclosure, copying or taking of any action in reliance on the contents of
this information is strictly prohibited. If you have received this
transmission in error, please immediately notify us by telephone to arrange
for return of the documents.
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, May 05, 2016 11:34 AM
To: [email protected]
Subject: RE: underground pipe under building footings
Rocci - There is no restriction regarding running lead-in piping under
footings. The restriction is how far into the building you run the line. The
concern is the damage created by the failure of a (normally) large diameter
fire main, as well as the extensive downtime required to repair such a main
if it were located a large distance from the outside of the building.
Generally speaking you are to bring the main up as close to the outside wall
as practical given your circumstances. Exceptions are granted if you rout
the pipe in a trench in the building floor with a removable cover.
NFA 24 or chapter 10 of NFPA 13 will give you this guidance.
In your situation I'd want to know if you are crossing under the narrow
dimension of the ADA ramp or if the entire ramp covers the pipe. In either
case I don't think you violate NFPA guidance, per se. But if there's a way
to avoid having the entire ramp over this main it should be considered.
I.e., it's more of a best practices issue.
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Thursday, May 5, 2016 1:24 PM
To: [email protected]
Subject: underground pipe under building footings
Before I go digging through a bunch of books I figured I'd try and save some
time by asking all you EXPERTS. Does anyone know which code states
underground fire service can't run under footings? We have a project where a
chemical bunker is being built and the ADA accessible ramp up to the bunker
is being built directly over an (e) 10" C-900 fire service and our new tap
that is going to feed the system in the bunker.
Thanks in advance for your responses.
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
[email protected]
www.norcalfire.com <http://www.norcalfire.com/>
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org