The problem with A.8.6.3.2.3 is that it only shows the one sprinkler. What
I'm concerned about is the distance between sprinklers B and C. In example
3 all the sprinklers are spaced correctly from the walls but B and C are
21'-2 1/2" apart. The way I understand it, they still need to be 15'-0"
along that wall, even though they're spaced correctly from every wall. Is
that correct?


James


On Friday, June 10, 2016, Brian Harris <[email protected]> wrote:

> Check out A.8.6.3.2.3 it should shed some light on it.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>]
> *On Behalf Of *James Litvak
> *Sent:* Friday, June 10, 2016 1:45 PM
> *To:* [email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>
> *Subject:* Angled Wall Spacing
>
>
>
> I am wondering if I've been thinking about sprinkler spacing along angled
> walls properly. What I mean is walls not at a right angle. The PDF I made
> in the link below really helps explain it. In example 1, four heads are
> spaced correctly at 225 sq. ft. In examples 2 and 3 one of the walls is
> angled. My question is, are either example 2 or 3 correct, or are they both
> wrong? My thought is that example 2 is incorrect, and for example 3 to be
> correct there would need to be an additional sprinkler along the angled
> wall between sprinklers B and C.
>
> https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0
>
>
>
> James
>