I'll chime in as well.
Example 3 is closer to being correct, as the sprinklers at B and C
aren't more than 7'-6" from a wall, measured perpendicular to the wall.
The error, to me, is the distance of 21'-2½" between B and C. I don't
see how that would be allowable, even if you were using extended
coverage sprinklers. Table 8.8.2.1.2 limits the distance between such
sprinklers, with the maximum being 20'-0" in OH and LH occupancies.
I don't see how that would be allowed.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 06/10/2016 12:51 PM, Ben Young wrote:
Agreed Tony.
On Friday, June 10, 2016, Tony Eggster <[email protected]
<mailto:[email protected]>> wrote:
#2 & #3 are both wrong.
#2 is spaced too far, measured perpendicularly, from the angled wall.
#3 will require an additional sprinkler between B and C. If you
draw a 15X15 square template on your drawings you will see an
obvious void of sprinkler coverage requiring protection.
On Fri, Jun 10, 2016 at 12:20 PM, James Litvak
<[email protected]
<javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
The problem with A.8.6.3.2.3 is that it only shows the one
sprinkler. What I'm concerned about is the distance between
sprinklers B and C. In example 3 all the sprinklers are spaced
correctly from the walls but B and C are 21'-2 1/2" apart. The
way I understand it, they still need to be 15'-0" along that
wall, even though they're spaced correctly from every wall. Is
that correct?
James
On Friday, June 10, 2016, Brian Harris
<[email protected]
<javascript:_e(%7B%7D,'cvml','[email protected]');>>
wrote:
Check out A.8.6.3.2.3 it should shed some light on it.
*Brian Harris, CET*
BVS Systems Inc.
bvssytemsinc.com <http://bvssystemsinc.com/>
*From:*Sprinklerforum
[mailto:[email protected]]
*On Behalf Of *James Litvak
*Sent:* Friday, June 10, 2016 1:45 PM
*To:* [email protected]
*Subject:* Angled Wall Spacing
I am wondering if I've been thinking about sprinkler
spacing along angled walls properly. What I mean is walls
not at a right angle. The PDF I made in the link below
really helps explain it. In example 1, four heads are
spaced correctly at 225 sq. ft. In examples 2 and 3 one of
the walls is angled. My question is, are either example 2
or 3 correct, or are they both wrong? My thought is that
example 2 is incorrect, and for example 3 to be correct
there would need to be an additional sprinkler along the
angled wall between sprinklers B and C.
https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0
James
_______________________________________________
Sprinklerforum mailing list
[email protected]
<javascript:_e(%7B%7D,'cvml','[email protected]');>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org