Good point. So use round ones on first ex. 1, since it's approved and
measure the area of dry floor/total area for 'inherent shadow area'.
Then do the same for the other two!
On Jun 10, 2016 4:08 PM, "Tony Eggster" <[email protected]> wrote:

> You wouldn't want to use a round one since spacing is determined by LxW.
> Rectangles are your friend (square in this case).
>
> On Fri, Jun 10, 2016 at 2:00 PM, Brad Casterline <[email protected]>
> wrote:
>
>> I like Tony's idea of a template but what if you used a round one with
>> radius=7.5 feet and used it at A,B,C,D in all three examples?
>> On Jun 10, 2016 2:58 PM, "Parsley Consulting" <[email protected]>
>> wrote:
>>
>>> I'll chime in as well.
>>>
>>> Example 3 is closer to being correct, as the sprinklers at B and C
>>> aren't more than 7'-6" from a wall, measured perpendicular to the wall.
>>>
>>> The error, to me, is the distance of 21'-2½" between B and C.  I don't
>>> see how that would be allowable, even if you were using extended coverage
>>> sprinklers.  Table 8.8.2.1.2 limits the distance between such sprinklers,
>>> with the maximum being 20'-0" in OH and LH occupancies.
>>>
>>> I don't see how that would be allowed.
>>>
>>> *Ken Wagoner, SET Parsley Consulting*
>>>
>>>
>>>
>>> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
>>> 760-745-6181 <760-745-6181> Visit our website
>>> <http://www.parsleyconsulting.com/> *
>>> On 06/10/2016 12:51 PM, Ben Young wrote:
>>>
>>> Agreed Tony.
>>>
>>> On Friday, June 10, 2016, Tony Eggster < <[email protected]>
>>> [email protected]> wrote:
>>>
>>>> #2 & #3 are both wrong.
>>>>
>>>> #2 is spaced too far, measured perpendicularly, from the angled wall.
>>>>
>>>> #3 will require an additional sprinkler between B and C. If you draw a
>>>> 15X15 square template on your drawings you will see an obvious void of
>>>> sprinkler coverage requiring protection.
>>>>
>>>> On Fri, Jun 10, 2016 at 12:20 PM, James Litvak <[email protected]>
>>>> wrote:
>>>>
>>>>> The problem with A.8.6.3.2.3 is that it only shows the one
>>>>> sprinkler. What I'm concerned about is the distance between sprinklers B
>>>>> and C. In example 3 all the sprinklers are spaced correctly from the walls
>>>>> but B and C are 21'-2 1/2" apart. The way I understand it, they still need
>>>>> to be 15'-0" along that wall, even though they're spaced correctly from
>>>>> every wall. Is that correct?
>>>>>
>>>>>
>>>>> James
>>>>>
>>>>>
>>>>> On Friday, June 10, 2016, Brian Harris <[email protected]>
>>>>> wrote:
>>>>>
>>>>>> Check out A.8.6.3.2.3 it should shed some light on it.
>>>>>>
>>>>>>
>>>>>>
>>>>>> *Brian Harris, CET*
>>>>>>
>>>>>> BVS Systems Inc.
>>>>>>
>>>>>> bvssytemsinc.com <http://bvssystemsinc.com/>
>>>>>>
>>>>>>
>>>>>>
>>>>>> *From:* Sprinklerforum [mailto:
>>>>>> [email protected]] *On Behalf Of *James
>>>>>> Litvak
>>>>>> *Sent:* Friday, June 10, 2016 1:45 PM
>>>>>> *To:* [email protected]
>>>>>> *Subject:* Angled Wall Spacing
>>>>>>
>>>>>>
>>>>>>
>>>>>> I am wondering if I've been thinking about sprinkler spacing along
>>>>>> angled walls properly. What I mean is walls not at a right angle. The 
>>>>>> PDF I
>>>>>> made in the link below really helps explain it. In example 1, four heads
>>>>>> are spaced correctly at 225 sq. ft. In examples 2 and 3 one of the walls 
>>>>>> is
>>>>>> angled. My question is, are either example 2 or 3 correct, or are they 
>>>>>> both
>>>>>> wrong? My thought is that example 2 is incorrect, and for example 3 to be
>>>>>> correct there would need to be an additional sprinkler along the angled
>>>>>> wall between sprinklers B and C.
>>>>>>
>>>>>>
>>>>>> <https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0>
>>>>>> https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0
>>>>>>
>>>>>>
>>>>>>
>>>>>> James
>>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>
>>>>>
>>>>
>>>
>>> --
>>>
>>> Benjamin Young
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing 
>>> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org