Agreed Tony.

On Friday, June 10, 2016, Tony Eggster <[email protected]> wrote:

> #2 & #3 are both wrong.
>
> #2 is spaced too far, measured perpendicularly, from the angled wall.
>
> #3 will require an additional sprinkler between B and C. If you draw a
> 15X15 square template on your drawings you will see an obvious void of
> sprinkler coverage requiring protection.
>
> On Fri, Jun 10, 2016 at 12:20 PM, James Litvak <[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>
>> The problem with A.8.6.3.2.3 is that it only shows the one
>> sprinkler. What I'm concerned about is the distance between sprinklers B
>> and C. In example 3 all the sprinklers are spaced correctly from the walls
>> but B and C are 21'-2 1/2" apart. The way I understand it, they still need
>> to be 15'-0" along that wall, even though they're spaced correctly from
>> every wall. Is that correct?
>>
>>
>> James
>>
>>
>> On Friday, June 10, 2016, Brian Harris <[email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>>
>>> Check out A.8.6.3.2.3 it should shed some light on it.
>>>
>>>
>>>
>>> *Brian Harris, CET*
>>>
>>> BVS Systems Inc.
>>>
>>> bvssytemsinc.com <http://bvssystemsinc.com/>
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:
>>> [email protected]] *On Behalf Of *James
>>> Litvak
>>> *Sent:* Friday, June 10, 2016 1:45 PM
>>> *To:* [email protected]
>>> *Subject:* Angled Wall Spacing
>>>
>>>
>>>
>>> I am wondering if I've been thinking about sprinkler spacing along
>>> angled walls properly. What I mean is walls not at a right angle. The PDF I
>>> made in the link below really helps explain it. In example 1, four heads
>>> are spaced correctly at 225 sq. ft. In examples 2 and 3 one of the walls is
>>> angled. My question is, are either example 2 or 3 correct, or are they both
>>> wrong? My thought is that example 2 is incorrect, and for example 3 to be
>>> correct there would need to be an additional sprinkler along the angled
>>> wall between sprinklers B and C.
>>>
>>>
>>> https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0
>>>
>>>
>>>
>>> James
>>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>

-- 