I like Tony's idea of a template but what if you used a round one with
radius=7.5 feet and used it at A,B,C,D in all three examples?
On Jun 10, 2016 2:58 PM, "Parsley Consulting" <[email protected]>
wrote:

> I'll chime in as well.
>
> Example 3 is closer to being correct, as the sprinklers at B and C aren't
> more than 7'-6" from a wall, measured perpendicular to the wall.
>
> The error, to me, is the distance of 21'-2½" between B and C.  I don't see
> how that would be allowable, even if you were using extended coverage
> sprinklers.  Table 8.8.2.1.2 limits the distance between such sprinklers,
> with the maximum being 20'-0" in OH and LH occupancies.
>
> I don't see how that would be allowed.
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 <760-745-6181> Visit our website
> <http://www.parsleyconsulting.com/> *
> On 06/10/2016 12:51 PM, Ben Young wrote:
>
> Agreed Tony.
>
> On Friday, June 10, 2016, Tony Eggster <[email protected]>
> wrote:
>
>> #2 & #3 are both wrong.
>>
>> #2 is spaced too far, measured perpendicularly, from the angled wall.
>>
>> #3 will require an additional sprinkler between B and C. If you draw a
>> 15X15 square template on your drawings you will see an obvious void of
>> sprinkler coverage requiring protection.
>>
>> On Fri, Jun 10, 2016 at 12:20 PM, James Litvak <[email protected]>
>> wrote:
>>
>>> The problem with A.8.6.3.2.3 is that it only shows the one
>>> sprinkler. What I'm concerned about is the distance between sprinklers B
>>> and C. In example 3 all the sprinklers are spaced correctly from the walls
>>> but B and C are 21'-2 1/2" apart. The way I understand it, they still need
>>> to be 15'-0" along that wall, even though they're spaced correctly from
>>> every wall. Is that correct?
>>>
>>>
>>> James
>>>
>>>
>>> On Friday, June 10, 2016, Brian Harris <[email protected]>
>>> wrote:
>>>
>>>> Check out A.8.6.3.2.3 it should shed some light on it.
>>>>
>>>>
>>>>
>>>> *Brian Harris, CET*
>>>>
>>>> BVS Systems Inc.
>>>>
>>>> bvssytemsinc.com <http://bvssystemsinc.com/>
>>>>
>>>>
>>>>
>>>> *From:* Sprinklerforum [mailto:
>>>> [email protected]] *On Behalf Of *James
>>>> Litvak
>>>> *Sent:* Friday, June 10, 2016 1:45 PM
>>>> *To:* [email protected]
>>>> *Subject:* Angled Wall Spacing
>>>>
>>>>
>>>>
>>>> I am wondering if I've been thinking about sprinkler spacing along
>>>> angled walls properly. What I mean is walls not at a right angle. The PDF I
>>>> made in the link below really helps explain it. In example 1, four heads
>>>> are spaced correctly at 225 sq. ft. In examples 2 and 3 one of the walls is
>>>> angled. My question is, are either example 2 or 3 correct, or are they both
>>>> wrong? My thought is that example 2 is incorrect, and for example 3 to be
>>>> correct there would need to be an additional sprinkler along the angled
>>>> wall between sprinklers B and C.
>>>>
>>>>
>>>> https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0
>>>>
>>>>
>>>>
>>>> James
>>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>
>
> --
>
> Benjamin Young
>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to