Oh, no sh#t.   Next to copper, blipped right over it.

SML

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Monday, August 01, 2016 1:38 PM
To: [email protected]
Subject: RE: C-factor for stainless steel

NFPA 13, 2013 ed. Table 23.4.4.7.1, C Value 150.

Thank you,
 
Bob Knight, CET III
208-318-3057
 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, August 01, 2016 2:10 PM
To: [email protected]
Subject: C-factor for stainless steel

Does anyone know the C-factor of stainless steel and/or have a reference to a 
materials standard that substantiates that value?

 

Thanks,

Steve L.