Ha! I'm going to get people to flush all the toilets at the same time and
destroy your precision. 3/100th of a pound in a calculation based on a
fairy tale developed from a bouncing gauge with an allowable degree of
accuracy plus/minus 3%. I see Scan giving a lecture on calculations, right
elbow in his left had while the forearm and right hand describe an arch of
25 or so degrees, representing the gauge during a pitot test.

On Mon, Aug 1, 2016 at 3:45 PM, Brad Casterline <[email protected]>
wrote:

> Ok, lol, thanks.
> And a correction, you would need the Absolute Roughness of SS to do a
> Darcy.
> Mistakes like that is not the reason Bradley drinks, he drinks because he
> likes the buzz
> :)
> On Aug 1, 2016 5:35 PM, "Steve Leyton" <[email protected]> wrote:
>
>> We have an over-zealous plans reviewer worried about the in-building
>> riser sweep we use to transition from UG to OH.   We’ve spent 2 man-hours
>> to account for a .03 PSI pressure differential.  But righteousness has
>> prevailed and we can add a node and document the sweep now, so our plans
>> reviewer should be able to sleep for the rest of the week.   I’m
>> embarrassed at our sloppiness, using 140 for 10 critical feet of pipe and
>> whatnot.
>>
>>
>>
>> This is why Chapter 17 of my great novel is tentatively titled “Why
>> Stevie Drinks”.
>>
>>
>>
>> SML
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *Brad
>> Casterline
>> *Sent:* Monday, August 01, 2016 3:26 PM
>> *To:* [email protected]
>> *Subject:* Re: C-factor for stainless steel
>>
>>
>>
>> Just curious about the application Steve, if it's not too proprietary?
>> I was going to guess foam concentrate piping but I think that requires
>> Darcy instead of Hazen whereby you would need the friction factor instead
>> of the c-factor...
>> So, uhhh????
>>
>> Brad
>>
>> On Aug 1, 2016 5:05 PM, "[email protected]" <[email protected]>
>> wrote:
>>
>> Don't feel bad, I went through the exact same exercise last October. LOL.
>> Right there the whole time but read over it a half dozen times until
>> someone on this form was kind enough to point it out to me.
>>
>>
>>
>>
>>
>> BK
>>
>>
>>
>> ----- Reply message -----
>> From: "Mark Phillips" <[email protected]>
>> To: "[email protected]" <
>> [email protected]>
>> Subject: C-factor for stainless steel
>> Date: Mon, Aug 1, 2016 3:51 PM
>>
>>
>>
>> It's a Monday for sure for me
>>
>>
>>
>> Sent from my Verizon 4G LTE Droid
>>
>> On Aug 1, 2016 5:49 PM, Steve Leyton <[email protected]> wrote:
>>
>> Oh, no sh#t.   Next to copper, blipped right over it.
>>
>>
>>
>> SML
>>
>>
>>
>> -----Original Message-----
>>
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Bob
>>
>> Sent: Monday, August 01, 2016 1:38 PM
>>
>> To: [email protected]
>>
>> Subject: RE: C-factor for stainless steel
>>
>>
>>
>> NFPA 13, 2013 ed. Table 23.4.4.7.1, C Value 150.
>>
>>
>>
>> Thank you,
>>
>>
>>
>> Bob Knight, CET III
>>
>> 208-318-3057
>>
>>
>>
>>
>>
>> -----Original Message-----
>>
>> From: Sprinklerforum [mailto:[email protected]]
>>
>> On Behalf Of Steve Leyton
>>
>> Sent: Monday, August 01, 2016 2:10 PM
>>
>> To: [email protected]
>>
>> Subject: C-factor for stainless steel
>>
>>
>>
>> Does anyone know the C-factor of stainless steel and/or have a reference to 
>> a materials standard that substantiates that value?
>>
>>
>>
>>
>>
>>
>>
>> Thanks,
>>
>>
>>
>> Steve L.
>>
>>
>>
>>
>>
>> _______________________________________________
>>
>> Sprinklerforum mailing list
>>
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>>
>> Sprinklerforum mailing list
>>
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> _______________________________________________
>>
>> Sprinklerforum mailing list
>>
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to