How did you answer that question Ken? The only thing I know about deflector
distance is minimum and maximum. I don't understand 'required'.
On Aug 1, 2016 6:46 PM, "rongreenman ." <[email protected]> wrote:

> Ha! I'm going to get people to flush all the toilets at the same time and
> destroy your precision. 3/100th of a pound in a calculation based on a
> fairy tale developed from a bouncing gauge with an allowable degree of
> accuracy plus/minus 3%. I see Scan giving a lecture on calculations, right
> elbow in his left had while the forearm and right hand describe an arch of
> 25 or so degrees, representing the gauge during a pitot test.
>
> On Mon, Aug 1, 2016 at 3:45 PM, Brad Casterline <[email protected]>
> wrote:
>
>> Ok, lol, thanks.
>> And a correction, you would need the Absolute Roughness of SS to do a
>> Darcy.
>> Mistakes like that is not the reason Bradley drinks, he drinks because he
>> likes the buzz
>> :)
>> On Aug 1, 2016 5:35 PM, "Steve Leyton" <[email protected]>
>> wrote:
>>
>>> We have an over-zealous plans reviewer worried about the in-building
>>> riser sweep we use to transition from UG to OH.   We’ve spent 2 man-hours
>>> to account for a .03 PSI pressure differential.  But righteousness has
>>> prevailed and we can add a node and document the sweep now, so our plans
>>> reviewer should be able to sleep for the rest of the week.   I’m
>>> embarrassed at our sloppiness, using 140 for 10 critical feet of pipe and
>>> whatnot.
>>>
>>>
>>>
>>> This is why Chapter 17 of my great novel is tentatively titled “Why
>>> Stevie Drinks”.
>>>
>>>
>>>
>>> SML
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:
>>> [email protected]] *On Behalf Of *Brad
>>> Casterline
>>> *Sent:* Monday, August 01, 2016 3:26 PM
>>> *To:* [email protected]
>>> *Subject:* Re: C-factor for stainless steel
>>>
>>>
>>>
>>> Just curious about the application Steve, if it's not too proprietary?
>>> I was going to guess foam concentrate piping but I think that requires
>>> Darcy instead of Hazen whereby you would need the friction factor instead
>>> of the c-factor...
>>> So, uhhh????
>>>
>>> Brad
>>>
>>> On Aug 1, 2016 5:05 PM, "[email protected]" <[email protected]>
>>> wrote:
>>>
>>> Don't feel bad, I went through the exact same exercise last October.
>>> LOL. Right there the whole time but read over it a half dozen times until
>>> someone on this form was kind enough to point it out to me.
>>>
>>>
>>>
>>>
>>>
>>> BK
>>>
>>>
>>>
>>> ----- Reply message -----
>>> From: "Mark Phillips" <[email protected]>
>>> To: "[email protected]" <
>>> [email protected]>
>>> Subject: C-factor for stainless steel
>>> Date: Mon, Aug 1, 2016 3:51 PM
>>>
>>>
>>>
>>> It's a Monday for sure for me
>>>
>>>
>>>
>>> Sent from my Verizon 4G LTE Droid
>>>
>>> On Aug 1, 2016 5:49 PM, Steve Leyton <[email protected]> wrote:
>>>
>>> Oh, no sh#t.   Next to copper, blipped right over it.
>>>
>>>
>>>
>>> SML
>>>
>>>
>>>
>>> -----Original Message-----
>>>
>>> From: Sprinklerforum 
>>> [mailto:[email protected]] On Behalf Of Bob
>>>
>>> Sent: Monday, August 01, 2016 1:38 PM
>>>
>>> To: [email protected]
>>>
>>> Subject: RE: C-factor for stainless steel
>>>
>>>
>>>
>>> NFPA 13, 2013 ed. Table 23.4.4.7.1, C Value 150.
>>>
>>>
>>>
>>> Thank you,
>>>
>>>
>>>
>>> Bob Knight, CET III
>>>
>>> 208-318-3057
>>>
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>>
>>> From: Sprinklerforum [mailto:[email protected]]
>>>
>>> On Behalf Of Steve Leyton
>>>
>>> Sent: Monday, August 01, 2016 2:10 PM
>>>
>>> To: [email protected]
>>>
>>> Subject: C-factor for stainless steel
>>>
>>>
>>>
>>> Does anyone know the C-factor of stainless steel and/or have a reference to 
>>> a materials standard that substantiates that value?
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> Thanks,
>>>
>>>
>>>
>>> Steve L.
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>>
>>> Sprinklerforum mailing list
>>>
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>>>
>>> Sprinklerforum mailing list
>>>
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>>
>>> Sprinklerforum mailing list
>>>
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>
>
> --
> Ron Greenman
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
> _______________________________________________