Why does a 2-story bldg. need a standpipe? Does your current design use the stairs for your sprinkler risers?
You'll may need a different pump due to pressure and possibly flow rate increase for standpipes versus sprinkler flow. If you design system risers routed in chases or other avenues for distribution now you need to be providing combination standpipe risers in the stairs. Why is an architect dictating what you provide as far as being a combined standpipe/riser? Sometimes it makes better sense to leave the standpipes separate from the sprinklers. So there are a lot of things to consider. Or just throw out what you did and start over and bill them EXTRA. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, August 09, 2016 8:21 AM To: [email protected] Subject: Combination Standpipes [EXTERNAL] Hypothetical question: You've completely designed a (2) story school, 6 zones with a pump, and now the owner/architect has decided to had combination standpipes to the job. What would be your thoughts on the amount of work involved? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935