150 PSI Churn, 1250 GPM @ 149 PSI is what I use for non high-rise standpipe
hydraulics flowing 1-5 FDV's.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Monday, September 12, 2016 3:21 PM
To: [email protected]
Subject: Fire Truck Supply @ FDC

 

Is there a "standard" GPM @ PSI used for a standpipe calc with regard to
what the fire truck will provide? I called the local AHJ and all he would
say is they provide 150psi, didn't know the gpm or even the hose size for
that matter. Any help would be greatly appreciated.

 