Do you also include the friction loss in the hose from the hose valve to
the end nozzle?  NFPA 14 (07ed) Table A.7.8 states that it takes 123psi @
250gpm at the valve outlet to account for 150ft of 2 ½” hose. Where does it
end?  We typically calc 100psi@250 gpm through the valve to the FDC
connection and this is fine with our AHJ’s.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Mark Phillips
*Sent:* Monday, September 12, 2016 2:29 PM
*To:* [email protected]
*Subject:* RE: Fire Truck Supply @ FDC



Also include the friction lose in hose from hydrant to truck  / truck to FDC

Mark

*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Matt Grise
*Sent:* Monday, September 12, 2016 3:26 PM
*To:* [email protected]
*Subject:* RE: Fire Truck Supply @ FDC



NFPA 14 will dictate your GPM. The hose size and truck performance are all
info items to get from the FD.



In the past, I have specified that we need 150psi at the FDC inlet – that
takes some of the guesswork out if it for us (since they could come with
different hose lengths/sizes). I have not met much pushback from FD’s with
that approach – but it would not hurt to check before test day.



But as previously suggested we use 150@0; 149@ required flow



Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
*Alliance Fire Protection*

130 w 9th Ave.
North Kansas City, MO 64116


**Licensed in KS & MO*



913.888.0647 ph
913.888.0618 f
913.526.7443 cell
*www. AFPsprink.com*





*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Brian
Harris
*Sent:* Monday, September 12, 2016 2:21 PM
*To:* [email protected]
*Subject:* Fire Truck Supply @ FDC



Is there a “standard” GPM @ PSI used for a standpipe calc with regard to
what the fire truck will provide? I called the local AHJ and all he would
say is they provide 150psi, didn’t know the gpm or even the hose size for
that matter. Any help would be greatly appreciated.



*Brian Harris, CET*

BVS Systems Inc.

Design Manager

bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to