That’s why I always put a calibrated gauge on the hydrant and a tapped
swivel and calibrated gauge on the FDC.

We usually get spare pumps or out of service pieces for our tests, never
trust the pump gauges.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark Phillips
Sent: Monday, September 12, 2016 3:29 PM
To: [email protected]
Subject: RE: Fire Truck Supply @ FDC

 

Also include the friction lose in hose from hydrant to truck  / truck to FDC

Mark

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Monday, September 12, 2016 3:26 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Fire Truck Supply @ FDC

 

NFPA 14 will dictate your GPM. The hose size and truck performance are all
info items to get from the FD. 

 

In the past, I have specified that we need 150psi at the FDC inlet – that
takes some of the guesswork out if it for us (since they could come with
different hose lengths/sizes). I have not met much pushback from FD’s with
that approach – but it would not hurt to check before test day.

 

But as previously suggested we use 150@0; 149@ required flow

 

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO 

 

913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Monday, September 12, 2016 2:21 PM
To: [email protected]
<mailto:[email protected]> 
Subject: Fire Truck Supply @ FDC

 

Is there a “standard” GPM @ PSI used for a standpipe calc with regard to
what the fire truck will provide? I called the local AHJ and all he would
say is they provide 150psi, didn’t know the gpm or even the hose size for
that matter. Any help would be greatly appreciated.

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to