Most FD's use 150 psi as a near universal starting point. It's what an FDC 
basically says "start me at".

If nozzle is not too high above FDC this isn't too bad. If nozzle is a number 
of floors up the operator will be ready to provide water before its needed. And 
it gets all of the now compressed air out of the system.

But once water is flowing, the pump operator will do field calc's to get the 
appropriate real pressure. Our standard 1 3/4 hose packs used 135 psi for 
friction loss and nozzle pressure. I suspect cities with bigger footprint 
buildings would use a 200' instead of 150' hose pack, getting you back to ~150 
psi at gated wye (2 1/2" X 1 1/2" X 1 1/2") I know an alternative is 50' 2 1/2" 
then wye, then standpipe bundles.

Our standard was for head pressure was 5 psi per floor. For all you three 
significant digit folks, this actually works out pretty close for 10-12' 
storeys. 

Field calc also includes friction loss between engine and FDC. 

And our standard calc included 25 psi for friction loss in the standpipe 
system. I later decided that this was way too much, but fire experience belied 
the numbers. The scheme we used did not result in too high nozzle pressure. 
Usually more pressure was requested by radio. Eventually I decided that hose 
lines were much more liable to have kinks in this setting compared to homes, 
restaurants, repair garages and so on. Compare a kink to a 1" 90 in a 1 1/2" 
sprinkler line. Lots of friction loss in a very short run.

So I didn't send a note to Training telling them no, we weren't seeing 25 psi 
f.l. in a five story standpipe at 200 gpm. 

NP + attack line FL + HP + 25 for standpipe and FDC + FL from engine to FDC = EP

To recap, 
-150 psi to get water flowing, 
-connect second 2 1/2" line to FDC and get it charged, 
-do field hydraulics, increase engine pressure, and reset relief valve ( or 
governor)
-adjust up 20 psi per each request from attack companies. 20 psi is about 
minimum that is noticeable. During active fire fighting you will not get a 
request for less.

After control, at some point pressure will be adjusted way down, per request. 

This is one FD's practice. It works well in low rise.

Best

Bruce Verhei

> On Sep 12, 2016, at 13:00, Brian Harris <[email protected]> wrote:
> 
> Thanks guys, much appreciated.
>  
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Brian Harris
> Sent: Monday, September 12, 2016 3:21 PM
> To: [email protected]
> Subject: Fire Truck Supply @ FDC
>  
> Is there a “standard” GPM @ PSI used for a standpipe calc with regard to what 
> the fire truck will provide? I called the local AHJ and all he would say is 
> they provide 150psi, didn’t know the gpm or even the hose size for that 
> matter. Any help would be greatly appreciated.
>  
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com
> Phone: 704.896.9989
> Fax: 704.896.1935
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to