Maybe a graphic will help.  Look at NFPA 13 (2013) Fig A.8.16.1.1.  In
particular, the "wet pipe and dry pipe system".  The FDC connects to the
header on the supply-side of the dry and wet system control valves.  Now
look at the "wet pipe system" - there is no control valve downstream of the
FDC tie-in location.  But you could add one there, since it's on the system
riser, not on the FDC pipe.   If you need to do maintenance on that system -
close the added valve.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, February 06, 2017 3:27 PM
To: [email protected]
Subject: RE: (1) FDC or (2)

 

I can't picture where your control valve is that you're proposing but unless
something has changed in NFPA 13, there are no control or isolation valves
allowed on an FDC line.  

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 



 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Ed Kramer
Sent: Monday, February 06, 2017 4:04 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: (1) FDC or (2) [EXTERNAL]

 

On a single-system wet system riser, there typically is no control valve
downstream of the FDC tie-in location.  By adding a control valve downstream
of the FDC tie-in location, system A can be shut down for repair/maintenance
by closing system A control valve.  FDC remains fully functional for system
B.  Similar in function to an underground supply/header with multiple
systems.  Now if either of the FDC pipes that connect the single FDC to the
2 system risers gets damaged, all bets are off.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected] <mailto:[email protected]> 
Sent: Monday, February 06, 2017 2:02 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: (1) FDC or (2)

 

How would you shut down potential supply flow from the common FDC to the out
of service system riser?

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Ed Kramer
Sent: Monday, February 06, 2017 2:34 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: (1) FDC or (2) [EXTERNAL]

 

Brian, If FDC supply pipe were run from a single FDC to both system risers,
and connected to the system risers between the BFP (or other supply check
valve) and a system control valve, either of the systems could be shut down
for maintenance/repair without impairing the FDC for the in-service system.
Each system riser would need its own FDC check valve.  Doing this might
require more bulk pipe and a couple more control valves.

 

Ed Kramer

Bamford Fire

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Monday, February 06, 2017 9:31 AM
To: [email protected]
<mailto:[email protected]> 
Subject: (1) FDC or (2)

 

I'm working on a storage building that because of the way the building was
built each "side" has its own Riser with its own FDC connection (picture a
big horseshoe shape). The architect has requested that a single FDC be
located on the corner of one of the building sides. Is it feasible to do
this and tie the systems together via the FDC pipe or does each Riser still
require its own FDC connection?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 