Better still, take a look at figure A.8.17.2.4.4(b) [2016]. One FDC, no control valve directly in the FDC line, and control valves for multiple risers.

No different than one FDC serving multiple floors in a high rise. One FDC, multiple isolation valves.

And, yes, this was added to the 2013 edition, and remains unchanged in the '16.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/>




***
On 02/06/2017 1:52 PM, Ed Kramer wrote:

Maybe a graphic will help. Look at NFPA 13 (2013) Fig A.8.16.1.1. In particular, the “wet pipe and dry pipe system”. The FDC connects to the header on the supply-side of the dry and wet system control valves. Now look at the “wet pipe system” – there is no control valve downstream of the FDC tie-in location. But you could add one there, since it’s on the system riser, not on the FDC pipe. If you need to do maintenance on that system – close the added valve.

*From:* Sprinklerforum [mailto:[email protected]] *On Behalf Of *[email protected]
*Sent:* Monday, February 06, 2017 3:27 PM
*To:* [email protected]
*Subject:* RE: (1) FDC or (2)

I can’t picture where your control valve is that you’re proposing but unless something has changed in NFPA 13, there are no control or isolation valves allowed on an FDC line.


*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]>

*From:* Sprinklerforum [mailto:[email protected]] *On Behalf Of *Ed Kramer
*Sent:* Monday, February 06, 2017 4:04 PM
*To:* [email protected] <mailto:[email protected]>
*Subject:* RE: (1) FDC or (2) [EXTERNAL]

On a single-system wet system riser, there typically is no control valve downstream of the FDC tie-in location. By adding a control valve downstream of the FDC tie-in location, system A can be shut down for repair/maintenance by closing system A control valve. FDC remains fully functional for system B. Similar in function to an underground supply/header with multiple systems. Now if either of the FDC pipes that connect the single FDC to the 2 system risers gets damaged, all bets are off.

*From:* Sprinklerforum [mailto:[email protected]] *On Behalf Of *[email protected] <mailto:[email protected]>
*Sent:* Monday, February 06, 2017 2:02 PM
*To:* [email protected] <mailto:[email protected]>
*Subject:* RE: (1) FDC or (2)

How would you shut down potential supply flow from the common FDC to the out of service system riser?


*Craig L. Prahl
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]>

*From:* Sprinklerforum [mailto:[email protected]] *On Behalf Of *Ed Kramer
*Sent:* Monday, February 06, 2017 2:34 PM
*To:* [email protected] <mailto:[email protected]>
*Subject:* RE: (1) FDC or (2) [EXTERNAL]

Brian, If FDC supply pipe were run from a single FDC to both system risers, and connected to the system risers between the BFP (or other supply check valve) and a system control valve, either of the systems could be shut down for maintenance/repair without impairing the FDC for the in-service system. Each system riser would need its own FDC check valve. Doing this might require more bulk pipe and a couple more control valves.

Ed Kramer

Bamford Fire

*From:* Sprinklerforum [mailto:[email protected]] *On Behalf Of *Brian Harris
*Sent:* Monday, February 06, 2017 9:31 AM
*To:* [email protected] <mailto:[email protected]>
*Subject:* (1) FDC or (2)

I’m working on a storage building that because of the way the building was built each “side” has its own Riser with its own FDC connection (picture a big horseshoe shape). The architect has requested that a single FDC be located on the corner of one of the building sides. Is it feasible to do this and tie the systems together via the FDC pipe or does each Riser still require its own FDC connection?

*Brian Harris, CET*

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to