The helipad is on the roof with nozzle surrounding it  . The fire dept asked if 
they could connect to the building FDC if need more foam at the helipad  (this 
feed 7 levels of wet pipe zones not directly to Foam system )

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: February-09-17 4:50 PM
To: [email protected]
Subject: RE: Foam - FDC

Is the foam system outdoors around the helipad? Monitors only?  What does the 
building FDC have to do with the helipad?

Trying to understand the relationship of the two areas to one another.

Need more info


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, February 09, 2017 4:47 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Foam - FDC [EXTERNAL]

I was just asked this question by the fire dept at a project where we designed 
a helipad foam system .

"A question has come up regarding the new helipad at the MRH.  We know there is 
a foam system installed that should provide approx. 10 minutes of foam mixture 
to the helipad upon activation of the system.  If foam is required for a longer 
period of time or if for some reason foam isn't being produced in the discharge 
from the monitors the question was asked would it be possible to supply a 
foam/water solution into the FDC on the building?  I realize this would 
probably not produce very nice foam but I would just like to know if there is 
any reason why a person could not attempt this if they felt it was required?  "


My  first response would be no , based on NFPA 16 2011  6.2.5 alone ,  any one 
else ran into this situation or offer any comments ?

Thanks  !


Colin Carew