Possibly provide extra foam, a tote near the Helipad? On Thu, Feb 9, 2017 at 3:46 PM, Colin Carew (Cambridge) < [email protected]> wrote:
> I was just asked this question by the fire dept at a project where we > designed a helipad foam system . > > > > “A question has come up regarding the new helipad at the MRH. We know > there is a foam system installed that should provide approx. 10 minutes of > foam mixture to the helipad upon activation of the system. If foam is > required for a longer period of time *or *if for some reason foam isn’t > being produced in the discharge from the monitors the question was asked > would it be possible to supply a foam/water solution into the FDC on the > building? I realize this would probably not produce very nice foam but I > would just like to know if there is any reason why a person could not > attempt this if they felt it was required? “ > > > > > > My first response would be no , based on NFPA 16 2011 6.2.5 alone , any > one else ran into this situation or offer any comments ? > > > > Thanks ! > > > > > > *Colin Carew* > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >